#128962 - 05/24/04 06:30 PM HPS bulb wattage
Duke Offline
Junior Member
Registered: 05/24/04
Posts: 1
Loc: Milwaukee, WI
Hi, guys (and gals?).
I have a coach lantern-style street fixture on my property that needs a bulb. It currently has a 100w LU100 and it may...MAY...be the wrong size. There's no label in the fixture, and when I tried to open up to look at the ballast I stopped short because the screws are VERY corroded and starting to break off if I go any further. My question is, let's say this fixture IS rated at 100 watts. Will it be ok to install a 70 watt bulb without damaging the ballast?

Thanx
Top
Tools for Electricians:
#128963 - 05/25/04 10:36 AM Re: HPS bulb wattage
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
In general no, you may not change the wattage of the lamp without changing the ballast also.

There are some exceptions for energy savings lamps, there are 320 watt MH lamps rated for use with 400 watt ballasts etc.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#128964 - 05/25/04 06:56 PM Re: HPS bulb wattage
Ralpha494 Offline
Member
Registered: 05/19/04
Posts: 73
Loc: Pewaukee,WI,USA
If it's a We Energies fixture it should have a little sticker on the street side with a "10" for 100w or a "7" for the 70w. That's how they tell.
Top
#128965 - 06/22/04 09:10 PM Re: HPS bulb wattage
Scott35 Offline

Broom Pusher and
Member
Registered: 10/19/00
Posts: 2707
Loc: Anaheim, CA. USA
Quote:

I have a coach lantern-style street fixture on my property that needs a bulb. It currently has a 100w LU100 and it may...MAY...be the wrong size.


Duke;

What happened to the original failed Lamp?
I am wondering why you might feel the wrong wattage Lamp had been used originally.

If the original Lamp was "Cycling" on and off for awhile, and gradually cycled off faster and faster until it just would not fully start (only had a bluish light output, then goes out within 30 seconds), this is normal end of life results for the HPS Lamp.

If it will not start now, but started and ran OK just a few days before, suspect the Ignitor.

If the Ballast windings are charred, suspect either incorrect Lamp wattage, failed capacitor, or both.

If you use a lower wattage Lamp on a higher wattage Ballast, it will fail sooner.
The cross over piont is at the 150 watt HPS - as there are 2 types here; 55 Volt and 100 Volt Lamps.
Use the wrong ones here and you will know very soon that there was a mismatching conflict!

Also using a Lamp / Ballast match where the values are very different (like 175 watt Lamp on a 400 watt Ballast, or vise verse) will bring sudden doom!

Scott35
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (cableguy619), 64 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals