#128949 - 05/13/04 01:59 AM Starting of motors  
Jacib  Offline
Junior Member
Joined: May 2004
Posts: 1
India
I have 2 questions
1.Normally a squirrel cage induction motor, is designed for a maximum starting current of 6-7 times its rated full load current.
What will be the starting current of the same motor, if it is started without any load using DOL(Direct On Line) starter?

2.Consider the case of a squirrel cage induction motor having a centrifugal pump (water application) as load. Normally before starting the delivery valve of the pump remains closed.
If the pump has a running load of X kW, what will be the starting load (kW) on the motor if it is started with a DOL starter?


Tools for Electricians:

#128950 - 05/17/04 04:33 PM Re: Starting of motors  
Radar  Offline
Member
Joined: Apr 2004
Posts: 349
Los Angeles, CA
I believe that "Starting Current" is simply a term that we give to the value of current a motor will draw when energized at rated voltage but the rotor is not turning. Thus, the instant an idle motor is energized, it will draw starting current, but as the motor rapidly comes up to speed, the current draw rapidly deminishes to normal run current.

The magnitude of the value of a motor's starting current should not change regardless of connected load. What does change is the duration time, how long the motor takes to spin up to normal speed. I've seen motors driving large fans that take so long to come up to speed (several seconds) that the overloads trip.

Starting a motor under full load increases the time the motor will need to come up to speed. This excess startup time can possibly overheat the motor if done repeatedly. So, centrifugal pump motors are frequestly started with a shut-off head to help aleviate this (not moving water = minimal load).

Hope this helps some,
Radar


There are 10 types of people. Those who know binary, and those who don't.

#128951 - 05/17/04 08:09 PM Re: Starting of motors  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...



Member Spotlight
NickD
NickD
Amish Country, PA
Posts: 46
Joined: March 2013
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.009s Queries: 14 (0.002s) Memory: 0.7504 MB (Peak: 0.8738 MB) Zlib enabled. Server Time: 2017-03-23 06:16:50 UTC