The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Yesterday at 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
1 registered (HotLine1), 341 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#128908 - 03/23/04 04:03 PM Selecting AIC
golf junkie Offline

Registered: 04/22/01
Posts: 511
Loc: York, NE
The customer wants a 480v, 125a MLO Sq. D NF panelboard for the service on an agricultural building. The PoCo transformers are pole mounted, delta-delta. Let's assume we have three 50kva transformers.

How do I select the correct aic breaker? The available sizes are;
65,000 aic
35,000 aic
18,000 aic


[This message has been edited by golf junkie (edited 03-23-2004).]

#128909 - 03/23/04 04:30 PM Re: Selecting AIC
winnie Offline

Registered: 09/15/03
Posts: 652
Loc: boston, ma
Take a look at
for an extremely basic introduction to short circuit calculations. Find out the transformer impedance, and presume every other impedance in the short is zero, to get a conservative approximate value.


#128910 - 03/23/04 05:19 PM Re: Selecting AIC
golf junkie Offline

Registered: 04/22/01
Posts: 511
Loc: York, NE
thanks jon, that was helpful

#128911 - 03/23/04 05:43 PM Re: Selecting AIC
Bjarney Offline

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
The utility should be able to provide that information for the service entrance location. Needed transfomer impedance data to estimate that value is not generally available to the electrician working downstream of the meter.

Also, that relieves the electrician of having to do short-circuit estimates for service-entrance equipment.

#128912 - 03/23/04 06:02 PM Re: Selecting AIC
Ron Offline

Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
Determine the full load current on the secondary, divide that number by the percent impedance of the transformer, and that gives you a conservative value at the secondary stabs of the xfmr. Depending on the length of the secondary conductors, that will further reduce the available fault current.
For example, 150000/480/1.73/.02=9030A of fault current at the secondary stabs.
You would be safe choosing the lowest AIC of the group.

#128913 - 03/24/04 06:34 AM Re: Selecting AIC
JBD Offline

Registered: 07/12/01
Posts: 599
Loc: WI, USA
Warning - the Square D NF panelboard is not rated for use on 480V delta systems. The NF panel has a slash rating of 480Y/277, so it can not be used on circuits with more than 277V to ground. You need to switch to their I-Line panel instead.

#128914 - 03/28/04 05:45 AM Re: Selecting AIC
PCBelarge Offline

Registered: 06/08/03
Posts: 657
Loc: Dobbs Ferry, NY, USA
That is good info that 'us' electricians can actually use.
That is very observant and a key pickup.

Pierre Belarge