#128876 - 03/08/04 06:06 PM Light Switches and Meter Readings
ThinkGood Offline
Member
Registered: 08/07/02
Posts: 1081
Loc: Milwaukee, WI
If a meter is placed in line with the two wires that make up the switched part of a lighting circuit, without the switch, should there be a reading of 120VAC?

To clarify, the "hot" is what would be switched (hopefully...) There is the conductor going to the top screw of the switch, and a conductor going to the bottom screw. Touch the two conductors together--by flipping the switch so to say--and the light goes on. What if a meter is placed between the two conductors, rather than a switch? Should there be any reading on the meter? Should the light go on?
Top
Tools for Electricians:
#128877 - 03/08/04 06:42 PM Re: Light Switches and Meter Readings
Scott35 Offline

Broom Pusher and
Member
Registered: 10/19/00
Posts: 2707
Loc: Anaheim, CA. USA
Thinkgood;

If you place the leads of a Volt Meter across the Terminals of a 1 Pole 1 Throw switch, which has either a Ballast or Incandescent Lamp on the Load side (which is not Barbequed / Failed Open - actually works...), you will find:
<OL TYPE=A>

[*] With Switch Closed - Zero Volts,

[*] With Switch Open - 120 Volts.
</OL>
FYI: above examples assume the system is 120 VAC, and the Switch Contacts are not pitted to death (make very good contact with less than 1 volt loss across the Switch).

So to answer your Q in full, if the Switch is removed and the Test Leads of a Volt Meter applied in its place, there will be a Voltage reading.
The Lamp will not light up, due to the Volt Meter's Impedance limiting the Current in this Series Circuit.
FYI: The Lamp and Meter will be in series, so it is now a series circuit. Highest Voltage will be measured across the highest Resistance / Impedance.

Hope this is what you are looking for!

Scott35
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top
#128878 - 03/08/04 06:50 PM Re: Light Switches and Meter Readings
Bjarney Offline
Moderator
Registered: 04/10/02
Posts: 2527
Loc: West-Southern Inner-Northeast ...
TG, that is a fundamental but important question. With the ususal high-impedance digital multimeter set to and jacked into a 200V-up AC-volt range, expect a reading of 120V with NO lighted lamp. But, if you set to and jack into an 2-amp & up AC-current scale, the meter should read the lamp load current {100 watts = ~0.8 amps} with a bright lamp.

The wiring position on plain-vanilla toggle-switch terminals usually does not matter.




[This message has been edited by Bjarney (edited 03-08-2004).]
Top
#128879 - 03/09/04 05:14 AM Re: Light Switches and Meter Readings
ThinkGood Offline
Member
Registered: 08/07/02
Posts: 1081
Loc: Milwaukee, WI
That's what I was looking for. Thank you, gentlemen.
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (cableguy619), 64 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals