The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 215 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#128876 - 03/08/04 06:06 PM Light Switches and Meter Readings
ThinkGood Offline
Member

Registered: 08/07/02
Posts: 1084
Loc: Milwaukee, WI
If a meter is placed in line with the two wires that make up the switched part of a lighting circuit, without the switch, should there be a reading of 120VAC?

To clarify, the "hot" is what would be switched (hopefully...) There is the conductor going to the top screw of the switch, and a conductor going to the bottom screw. Touch the two conductors together--by flipping the switch so to say--and the light goes on. What if a meter is placed between the two conductors, rather than a switch? Should there be any reading on the meter? Should the light go on?

Top
#128877 - 03/08/04 06:42 PM Re: Light Switches and Meter Readings
Scott35 Offline

Broom Pusher and
Member

Registered: 10/19/00
Posts: 2724
Loc: Anaheim, CA. USA
Thinkgood;

If you place the leads of a Volt Meter across the Terminals of a 1 Pole 1 Throw switch, which has either a Ballast or Incandescent Lamp on the Load side (which is not Barbequed / Failed Open - actually works...), you will find:


    [*] With Switch Closed - Zero Volts,

    [*] With Switch Open - 120 Volts.

FYI: above examples assume the system is 120 VAC, and the Switch Contacts are not pitted to death (make very good contact with less than 1 volt loss across the Switch).

So to answer your Q in full, if the Switch is removed and the Test Leads of a Volt Meter applied in its place, there will be a Voltage reading.
The Lamp will not light up, due to the Volt Meter's Impedance limiting the Current in this Series Circuit.
FYI: The Lamp and Meter will be in series, so it is now a series circuit. Highest Voltage will be measured across the highest Resistance / Impedance.

Hope this is what you are looking for!

Scott35
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Top
#128878 - 03/08/04 06:50 PM Re: Light Switches and Meter Readings
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
TG, that is a fundamental but important question. With the ususal high-impedance digital multimeter set to and jacked into a 200V-up AC-volt range, expect a reading of 120V with NO lighted lamp. But, if you set to and jack into an 2-amp & up AC-current scale, the meter should read the lamp load current {100 watts = ~0.8 amps} with a bright lamp.

The wiring position on plain-vanilla toggle-switch terminals usually does not matter.




[This message has been edited by Bjarney (edited 03-08-2004).]

Top
#128879 - 03/09/04 05:14 AM Re: Light Switches and Meter Readings
ThinkGood Offline
Member

Registered: 08/07/02
Posts: 1084
Loc: Milwaukee, WI
That's what I was looking for. Thank you, gentlemen.