The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Topic Options
Rate This Topic
#128738 - 11/14/03 04:55 AM tripped breaker re-setting
huungrycat Offline
Junior Member
Registered: 04/04/02
Posts: 7
Loc: myrtle beach,s.c.usa
a 3ph 480v motor tripped a breaker.a worker saw this and re-set the breaker.a short time the worker saw the breaker tripped again and tried to re-set the breaker.at this time the panel exploded knocking the worker to the ground.he recieved a severe electrical shock and burns which hospitalized him and put him in a burn unit.
how many times must a breaker trip before you call an electrican? 2 sure isnt good.
Top
Tools for Electricians:
#128739 - 11/14/03 07:43 AM Re: tripped breaker re-setting
JBD Offline
Member
Registered: 07/12/01
Posts: 599
Loc: WI, USA
You did not include enough information to provide an answer which is applicable to your situation.

Circuit breakers are tested and then listed based on:
Rated voltage
Applied voltage
Frame size
Trip unit type
Rated continuous current
Applied continuous current
Rated short circuit fault current
Applied short circuit fault current
Short circuit impedances
Type of fault (i.e. bolted, three phase)
Number of poles clearing the fault

Also you need to include the electrical and mechanical history of your breaker. This history should include the number of no-load operations, the number of full-load operations, and the number of short circuit operations.

In general, I believe breakers are only "rated" for 2 operations at their maximum short circuit rating.
Top
#128740 - 11/14/03 07:52 AM Re: tripped breaker re-setting
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2209
Loc: IL
In general OSHA says you must invetigate the cause of the trip before the breaker is reclosed.
_________________________
Don(resqcapt19)
Top
#128741 - 11/14/03 09:13 AM Re: tripped breaker re-setting
ThinkGood Offline
Member
Registered: 08/07/02
Posts: 1084
Loc: Milwaukee, WI
Top
#128742 - 11/14/03 03:30 PM Re: tripped breaker re-setting
Scott35 Offline

Broom Pusher and
Member
Registered: 10/19/00
Posts: 2724
Loc: Anaheim, CA. USA
Breaker was probably tripped and reset many, many, many-many-many times before this scenario.

Sounds like the frame failed to contain the arc (probably a bolted fault condition on the load side),
Or,

The AIC of the frame was highly exceeded,
Or,

The frame fell apart and caused an arc fault,
Or,

All of the above.

As pointed out by Don, find out why a breaker is tripping first. Then only after correcting the problem would the breaker be reset.
If it trips again, there are more problems to look for.

When 480 VAC Power Circuits are tripping, be REALLY careful when resetting breakers!!!
Find the fault(s) first!!!
Reset the breaker last!!! Do it only once!!!

Arc faults are very mean Animals!!! They are like Badgers:
Very belligerent, extremely fast, and most of all, very unforgiving!!

Scott35
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
01/23/17 12:27 AM
License exam
by TRUE POWER
01/22/17 11:33 PM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
2 registered (Admin, sparkyinak), 82 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals