The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Correct rotation, wrong sequence
by Potseal
Today at 03:14 PM
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 10
Potseal 9
sparkyinak 8
Texas_Ranger 7
Who's Online
0 registered (), 218 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#128729 - 11/07/03 04:46 PM Short circuit calc's
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
Scott (or anyone else): I glanced through you very informative technical resource area, but I could not find any examples of short circuit/fault current calculations. Would you mind showing me an example of one when you find the time? Thank you very much.
_________________________
Ryan Jackson,
Salt Lake City

Top
#128730 - 11/07/03 05:50 PM Re: Short circuit calc's
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
One simplified calculator is listed at http://www.bussmann.com/apen/software/ Available short-circuit currents are primarily controlled by various transformer impedances in power systems, which also cause voltage drop in AC-electrical circuits.

Top
#128731 - 11/10/03 04:17 AM Re: Short circuit calc's
Scott35 Offline

Broom Pusher and
Member

Registered: 10/19/00
Posts: 2724
Loc: Anaheim, CA. USA
SCA calcs (formulas) were something I should have compiled and posted in the Reference section, but strangely enough have yet to do so!


I'll see what can be compiled from the Bussman SPD documents for the three commonly used methods, then post ASAP.

Scott35
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Top
#128732 - 11/10/03 06:26 AM Re: Short circuit calc's
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
Scott: Thanks. Again, at your convienance. I hope I didn't come across as complaining about your very informative section, that was certainly not the intent.

Bjarney: Thanks. I have reviewed the site and found it quite helpful
_________________________
Ryan Jackson,
Salt Lake City

Top
#128733 - 01/05/04 01:10 AM Re: Short circuit calc's
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Ryan,
As a rule, PSCC(Prospective Short Circuit Current) is governed by this formula, as a very simplistic way of looking at it:
I(pscc)= V(oc) / Z.


[This message has been edited by Trumpy (edited 01-05-2004).]
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#128734 - 02/06/04 03:02 PM Re: Short circuit calc's
Ichabod Offline
Member

Registered: 05/24/03
Posts: 26
Loc: Statesboro, GA, USA
Easiest way is ignore primary and secondary conductor impedances since the transformer impedance is usually quite large compared to the wire impedance. Then it's just Ohm's law, I = E/Z, or I = (1/%Z)(FLA).

In other words, just divide FLA by Transformer PU impedance(%Z/100)

Example: For a typical 25 kva, 12kv to 120/240v transformer, Z% = 2.4%. I (SC) = 104.2/.024 = 4340A

BTW, some new pole mounted and some padmount transformers have impedances less than 2 percent.

Top
#128735 - 02/06/04 08:03 PM Re: Short circuit calc's
mighty_thor Offline
Member

Registered: 05/18/03
Posts: 13
Loc: san jose, ca, usa
There are different method of calculating
short circuits.
It depends what component are installed
on the system.

One book that help me a lot, whem I am
doing short circuit calculation is

"Electrical System analysis and design for
Industrial Plant by Irwin Lazar".

The examples are very easy to understand
and very applicable to modern electrical
system that exist today.

Top
#128736 - 02/13/04 08:37 PM Re: Short circuit calc's
Scott35 Offline

Broom Pusher and
Member

Registered: 10/19/00
Posts: 2724
Loc: Anaheim, CA. USA
Here's some "Quick 'N Dirty" SCA calc formulas, using the basic "Point-to-Point" method.

Available short-circuit symmetrical RMS current is found using the 6 steps described below:

Step 1; Determine the Transformer's Full-Load Amperes (I·fl):

3Ø Transformer

I·fl = KVA × 1000 / E·l-l × 1.732

1Ø Transformer

I·fl = KVA × 1000 / E·l-l

Step 2; Find the Transformer multiplier (M·tr):

M·tr = 100 / (%Z × 0.9)
where: %Z is the Transformer's Impedance.

Step 3; Determine the Transformer let-thru short circuit current (I·sc):

I·sc = I·fl × M·tr

FYI: Induction Motor contribution may be added to the above figure at this point.
An estimate for Motor contribution to SCA is:
4 to 6 × FLA of Motor(s).
LRA may also qualify.

Step 4; Calculate the "F" factor:

3Ø Faults:

F = 1.732 × L × I·3ø / C × E·l-l

1Ø L-L Faults on 1ph center tapped transformer:

F = 2 × L × I·l-l / C × E·l-l

1Ø L-N Faults on 1ph center tapped transformer:

F = 2 × L × I·l-n / C × E·l-n

where:
"L" = Length (feet) of conductor to the fault.
"C" = Constant from "Table C" of the Bussman manual (will add this later - big database!).
"I" = Available short circuit current at beginning of circuit.
"L-L" = Line-to-Line.
"L-N" = Line-to-Center Tapped "Neutral" conductor.
*Note: L-N fault current is higher than the L-L fault current at the secondary terminals of a 1Ø center tapped transformer. The short circuit current available for this case in step 4 should be adjusted at the transformer terminals as follows:
I·l-n = 1.5 × I·l-l at transformer terminals.


Step 5; Calculate "M" (multiplier):

M = 1 / 1 + F


Step 6; Calculate the available short circuit symmetrical RMS current at the point of fault (I·afc):

I·afc = I·sc × M

I'll post a few example SCA scenarios later when posting the "C" database.

Scott35
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Top
#128737 - 05/04/04 03:21 PM Re: Short circuit calc's
Frank Martino Offline
New Member

Registered: 05/04/04
Posts: 7
Loc: Middlebury, CT, USA
"Short Circuit Capacity: Basic Calculations and Transformer Sizing"
http://www.powerqualityanddrives.com/short_circuit_transformer/

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals