#128696 - 10/03/03 05:56 PM Portable generator - Seperatly derived or not
Ron Offline
Member
Registered: 03/13/02
Posts: 582
Loc: White Plains, NY
I will have a portable generator that will be on occasion connected as a separately derived source and at times not a separately derived source.
When I have a tool directly plugged into the generator mounted receptacle, it will be a separately derived system. When I have the generator recept connected to house wiring through a 2 pole transfer switch (neutral not switched), it will not be a separately derived source.
250.34(C) dictates that as a separately derived source, the grounded conductor must be bonded to the generator frame. As a non-separately derived source, it would not have its grounded conductor bonded to the frame.
Remember since all loads will be connected through the generator mounted receptacles, no connection of the frame to a grounding electrode system is required 250.34(C).

OK, now the theory question. How does the functionality and safety characteristics change if the neutral to frame remains connected or unconnected (only one way or the other) when the gen is used as a non-separately derived source and a separately derived source. I cannot grasp why it is necessary to change the generator from bonded to unbonded if I plug the tool into the gen directly or into a recept in my home (which is plugged into the gen through the xfer switch).
_________________________
Ron
Top
Tools for Electricians:
#128697 - 10/08/03 05:49 AM Re: Portable generator - Seperatly derived or not
Ron Offline
Member
Registered: 03/13/02
Posts: 582
Loc: White Plains, NY
To place some closure on this item, I cross posted it. The solution was right in front of my face. It is easiest to refer the post to the picture located at http://www.mikeholt.com/codeforum/ultimatebb.php?ubb=get_topic;f=7;t=000454;p=1#000002
I hope it isn't against etiquette to list another forum, sorry if it is.
_________________________
Ron
Top

Member Spotlight
Member Since: 10/07/00
Posts: 3417
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals