The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
ghost307 7
HotLine1 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 327 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#128499 - 04/21/03 11:19 PM neutral current
elecbob Offline

Registered: 08/23/02
Posts: 142
Loc: WA
Can anyone point me the way to the formula for calculating the neutral current in a 3 phase wye circuit?thanks

#128500 - 04/22/03 04:04 AM Re: neutral current
BPHgravity Offline

Registered: 04/08/03
Posts: 141
Loc: Port Charlotte, Florida
I do not know of any online versions of the calculation, but I will be happy to post it right here for you.

In = the square root of I^A+I^B+I^C-(IA*IB)-(IB*IC)-(IC*IA)

However, I have found that for field calculations, by determining the load of the greatest unbalance of any two phase loads will give you a very accurate value. EX: A=30amp, B=40amp, C=50amp. The greatest difference is 50-30= 20amp. If you perform the above calculation, the value comes to around 17.32amp. Not close enough for an exam question, but plenty clos enough for field calcs.
Bryan P. Holland, ECO.
Secretary - IAEI Florida Chapter

#128501 - 05/25/03 06:19 AM Re: neutral current
Ichabod Offline

Registered: 05/24/03
Posts: 26
Loc: Statesboro, GA, USA
gravity, why does that work? I know it does because I used my HP-11C calculator and assumed that the phases were 120 degrees apart and got the same answer. The way I do it is to convert the polar quantities into rectangular and total them, then convert back to polar. Using the HP it only takes a few seconds once you learn how to do it, faster than your method. If the currents are not 120 degrees apart, then there is a lot of difference in doing it my way and your way. For an electrician, probably doesn't matter. I was a substation test engineer commissioning protective relays and had to know very accurately what the residual currents were. But I am intriqued by your method. Thought at first it was symmetrical components, but ruled that out.