The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 84 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#128407 - 02/23/03 10:27 PM Ground fault current
Andre M Offline
Junior Member

Registered: 02/22/03
Posts: 8
Loc: Wheeling, IL
Problem recently posted for my class:

Heating element rated 240v 4800W (20A) has been connected to 120/208v grounded "Y" system between two phases (208v). - Everybody egrees now 3600W / 17.3A.
1. Midpoint of the element is shorted to ground assuming 0 (zero) resistance of ground fault. What total power is rreleased during ground fault?
2. What current flow to ground?

What is your opinion on asked numbers? - Is it too hard for master electrician?

Andre

Top
#128408 - 02/24/03 04:46 AM Re: Ground fault current
Gwz Offline
Member

Registered: 04/29/02
Posts: 199
Find ohms of the original.

R = E / I, R = 240V / 20A, R = 12 ohms.

Now this is used on a 208/120V system.

The Neutral of 208/120V system is intentionaly connected to Ground and you noted 0 restistance to ground, thus the circuit at midpoint is being operated as on 120V system.

1/2 of the 12 ohms is 6 ohms.

I on the 120v as now operating is;

I = E / R, I = 120V / 6R, I = 20A on each of the two sections of the ground faulted 240, 4800W, 20A heater operated on the 208V system.

Top
#128409 - 02/24/03 06:05 AM Re: Ground fault current
Andre M Offline
Junior Member

Registered: 02/22/03
Posts: 8
Loc: Wheeling, IL
Yes, thanks. Now a little harder second question. Find ground current.

Top
#128410 - 05/25/03 03:48 AM Re: Ground fault current
Ichabod Offline
Member

Registered: 05/24/03
Posts: 26
Loc: Statesboro, GA, USA
20 Amps.

Ichabod

Top
#128411 - 05/31/03 07:00 PM Re: Ground fault current
Scott35 Offline

Broom Pusher and
Member

Registered: 10/19/00
Posts: 2724
Loc: Anaheim, CA. USA
Should I draw this one up and post it in the Tech. Reference section?

Scott
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Top
#128412 - 06/01/03 06:36 AM Re: Ground fault current
Ichabod Offline
Member

Registered: 05/24/03
Posts: 26
Loc: Statesboro, GA, USA
Yes Scott, please do.

Ichabod

Top