The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 223 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#128365 - 01/25/03 08:22 PM Short Circuit 1000kva 3 ph 1.6% Impedance 277/480
HouseOfPower Offline
Member

Registered: 01/25/03
Posts: 11
Loc: Houston Texas
I have another question.

On a short circuit current of a 1000 kva, 3 phase transformerbank with a 1.6% impedance operating at 277/480

First I did: 1000 x 1000= 1,000,000 / 277

=3610
3610/ 1.732= 2084
2084/ .016= 130,272.38?

Did I goof up with the impedance? Shoul it be divided by the .016 or 1.6 ?

Top
#128366 - 01/25/03 10:50 PM Re: Short Circuit 1000kva 3 ph 1.6% Impedance 277/480
Scott35 Offline

Broom Pusher and
Member

Registered: 10/19/00
Posts: 2724
Loc: Anaheim, CA. USA
I came up with an SCA of 83,619.64 Amps at the Transformer (3Ø Bolted Fault, Infinite Primary, 0.9 of the %Z for tolerances).

Here's the formula I used to acheive the resulting 83619.64 amps:

1: Determine the Full-Load Amperes of the Transformer:

I(FLA) = KVA × 1000 ÷ E(L-L) × 1.73
[ "I(FLA)" = Full-Load Amperes, "E(L-L)" = Line-To-Line Voltage ]

2: Find Transformer's Multiplier:

Mpl. = 100 ÷ 0.9 × %Z
[ "Mpl." = Multiplier, "0.9" figures worst-case scenario tolerance of Impedance percentage ]

3: Determine Transformer's Let-Through Current:

I(SCA) = I(FLA) × Mpl.

So using your Transformer's ratings, here's what it looks like:

1: I(FLA) = 1204.2 Amps
( 1000 × 1000 ÷ 480 × 1.73 )

2: Mpl. = 69.44
( 100 ÷ 0.9 × 1.6 )

3: I(SCA) = 83619.644444- Amperes
( 1204.2 × 69.44 )

Check my math and let me know if there are any errors.

Scott35 S.E.T.
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Top
#128367 - 01/26/03 09:06 AM Re: Short Circuit 1000kva 3 ph 1.6% Impedance 277/480
Nick Offline
Member

Registered: 08/13/01
Posts: 603
Loc: Riverside, CA
Scott,
Your math checks out.
Just out of curiousity I ran this through some software programs. Here are the results:
Bussmann-83,531.135
EDR-83,532
This is using your .9 of %Z value.
Pretty close huh?

Top
#128368 - 01/26/03 09:15 AM Re: Short Circuit 1000kva 3 ph 1.6% Impedance 277/480
HouseOfPower Offline
Member

Registered: 01/25/03
Posts: 11
Loc: Houston Texas
Ok, I wasn't working the problem right. Looks like it is back to the drawing board. thanks

Top
#128369 - 01/26/03 11:22 AM Re: Short Circuit 1000kva 3 ph 1.6% Impedance 277/480
Scott35 Offline

Broom Pusher and
Member

Registered: 10/19/00
Posts: 2724
Loc: Anaheim, CA. USA
Nick,

Closer than I even expected!!!

I ran the numbers by hand! (feel free to make jokes or laugh!).

Scott35 S.E.T.
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Top
#128370 - 01/26/03 06:07 PM Re: Short Circuit 1000kva 3 ph 1.6% Impedance 277/480
Gwz Offline
Member

Registered: 04/29/02
Posts: 199
Given:
KVA = 1000
E = 480V
3Ø = 1.732
% Z = 1.6
.9 = factor if KVA great than 25

using continuous calculator input the formula would be:

KVA * 1000 / 480V / 1.732 = * 100 / 1.6%Z / .9 = SCA

1000*1000/480/1.732=*100/1.6/.9= 83531.135061158155846377555384484 short circuit amperes.

That is by using the calculator in Windows Acessories on the computer programs file.

Just think - - - Could have used 1.732050807568877293527446341115059 for the square root of 3.

Then it would be 83528.684778591690467180089771695 Short Circuit Amperes.

Top
#128371 - 01/26/03 06:58 PM Re: Short Circuit 1000kva 3 ph 1.6% Impedance 277/480
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
1.6%Z? That is one stiff transformer.

Padmount? Delta-Wye?

Top
#128372 - 01/26/03 07:09 PM Re: Short Circuit 1000kva 3 ph 1.6% Impedance 277/480
HouseOfPower Offline
Member

Registered: 01/25/03
Posts: 11
Loc: Houston Texas
After the 1.732 you multiply by 100

Where and how do you get that figure?

Top
#128373 - 01/26/03 07:14 PM Re: Short Circuit 1000kva 3 ph 1.6% Impedance 277/480
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
It's likely that is needed to convert 1.6% into 0.016 per-unit impedance.

Top
#128374 - 01/27/03 04:33 AM Re: Short Circuit 1000kva 3 ph 1.6% Impedance 277/480
Gwz Offline
Member

Registered: 04/29/02
Posts: 199
That is not the formula.

It is a way to keep using the ( hand ) calculator with-out stopping to enter a previous calculation into the final answer.

Of course the 1.6%Z sounds low for that KVA.

Maybe it's one of the super efficient transformer (super cooled coils) or that ( amorrous steel) [ I know that is not the correct spelling, but it is a special conductor/or/core used for some experimental transformers. It was mentioned in the EC&M magazine about 10 years ago.].

The local PoCo has 50KVA pad mounts with 0.9 %Z.

These 0.9 %Z units are 7.2KV/120/240V 1Ø 3W pad mounts.

[This message has been edited by Gwz (edited 01-27-2003).]