The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Today at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
sparkyinak 8
Texas_Ranger 8
Trumpy 6
Who's Online
0 registered (), 248 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#128324 - 01/18/03 04:33 PM Buck Boost KVA rating
maintenanceguy Offline
Member

Registered: 12/02/01
Posts: 303
Loc: Southern NJ, USA
Can somebody explain how to calculate the required KVA rating of a buck boost transformer?

Top
#128325 - 01/18/03 05:33 PM Re: Buck Boost KVA rating
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
There is a good section in http://www.federalpacific.com/literature/drytrans/FPTS-RTB-0701.pdf

Depends on series/parallel primary/secondary connections, 1ø or 3ø, 2- 3- 4-wire, delta or wye source/load.




[This message has been edited by Bjarney (edited 01-19-2003).]

Top
#128326 - 01/20/03 11:30 PM Re: Buck Boost KVA rating
Scott35 Offline

Broom Pusher and
Member

Registered: 10/19/00
Posts: 2724
Loc: Anaheim, CA. USA
Re: Figuring KVA rating for Buck / Boost Transformers:

Basically, the capacity - in Amperes - of the Secondary side is what determines the overall KVA rating for these setups.

These Transformers are simply small / low KVA rated ISOLATED TRANSFORMERS with low voltage Secondary Winding(s),
being connected in a fashion which creates an AUTOTRANSFORMER type setup.

The Primary Winding(s) do not carry the full KVA that is achieved through the new connection scheme - only a small amount of Apparent Power (Volt-Amps, or VA) is drawn in the Primary as compared to the total Apparent Power going to a load.
The Secondary side is the crucial player in these designs!

Along with increasing (or decreasing) the output Voltage, the Secondary Winding(s) will be carrying the load current - so the Winding(s) need to have capacity to do this.

A simple example for figuring the Maximum Line KVA of a Boost (or Buck) Transformer arrangement is shown below, using a normal Dry-Type Isolated Transformer (Primary Windings not Electrically connected to Secondary Windings):

Transformer Rating:
120/240 VAC (Pri) × 12/24 VAC (Sec) - 1 KVA @ 150° C maximum

Figuring the Line (Input) Voltage is 120 VAC, the Primary Windings are connected in Parallel (for 120 VAC).

Figure the Current Rating ( I ) of the Secondary side:

VA = KVA × 1000 - convert the Kilo Volt-Amps figure to Volt-Amps,

I = VA ÷ E - Find Current ( I ) by dividing Apparent Power ( VA) by the Voltage ( E ).
KVA = Isec × Ein ÷ 1000

For a connection with 132 VAC output ( + 12 Volts ), the Secondaries are connected in Parallel.
The KVA Rating will be:

Isec = 83.34 Amps
120 VAC × 83.34 Amps = 10,000.8 VA - or simply 10 KVA
Output will be 10 KVA @ 132 VAC

For a connection with 144 VAC output ( + 24 Volts ), the Secondaries are connected in Series.
The KVA Rating will be:

Isec = 41.67 Amps
120 VAC × 41.67 Amps = 5,000.4 VA - or simply 5 KVA
Output will be 5 KVA @ 144 VAC

The same calculations work for Voltage Reducing ("Buck") connections also.

If you have further questions, feel free to ask away!!!
Also, feel free to contact me directly via E-mail if needed.

Hoping this data is helpful enough to answer your question!

Scott35 s.e.t.
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Top
#128327 - 01/21/03 03:05 PM Re: Buck Boost KVA rating
maintenanceguy Offline
Member

Registered: 12/02/01
Posts: 303
Loc: Southern NJ, USA
beautiful

Thank you.

Top
#128328 - 01/24/03 04:01 AM Re: Buck Boost KVA rating
Scott35 Offline

Broom Pusher and
Member

Registered: 10/19/00
Posts: 2724
Loc: Anaheim, CA. USA
No problem!!!

I hope this stuff makes sense and is as helpful as possible to you and everyone else!

Scott35 S.E.T.
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Top
#128329 - 04/02/03 06:13 AM Re: Buck Boost KVA rating
engy Offline
Member

Registered: 06/25/02
Posts: 15
Loc: Minnesota
Wouldn't the 83.3A go through the 132V load for(11kVA)?

and the 41.7 A go through the 144V load for (6kVA)?