The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
2 registered (NORCAL, sparkyinak), 205 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#128260 - 01/02/03 10:39 AM Open Deltas
ronko Offline
Junior Member

Registered: 01/02/03
Posts: 1
Loc: Clark County, Nevada
Scott,
I've been going over transformer hookups, calcs for ocp, delta/wye voltage and current relationships but one thing I can't get a handle on is the reduction of transformer capacity using an open delta.
One situation calls out when using two single-phase transformers with a reduction at 87%(86.6), another when three single-phase transformers are used and one is removed for a reduction of 58%(57.7) and finally when sizing for load, equivalent to three transformers two transformers should be ratied up to 15.5%.
Please try to clarify
Thanks

Top
#128261 - 01/02/03 03:56 PM Re: Open Deltas
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
Examples: In the first case, If there were a pair 10-kVA transformers, their capacity is 17.3kVA, and not 20kVA

30,000 VA total nameplate for three pots
0.5774 = 1/sqrt3
17,321 VA rating using only two 10kVA pots

In the second case, if there was one transformer removed from a three 10kVA pots, there capacity is reduced to 17.3kVA

20,000 total nameplate VA for two pots
0.8660 = sqrt3/2
17,321 VA actual capacity for two pots

In the third case, for two transformers serving a 20kVA load, the total nameplate capacity needed is 23.1kVA

20,000 VA load - served by two pots
1.1547 = 2/sqrt3
23,094 VA total nameplate transformer capacity for the two pots; id est, two 10kVA pots cannot adequately serve a 20kVA load.


Cooper Power bulletin R201-90-2 may be a useful reference.




[This message has been edited by Bjarney (edited 01-02-2003).]

Top
#128262 - 01/05/03 04:57 AM Re: Open Deltas
Scott35 Offline

Broom Pusher and
Member

Registered: 10/19/00
Posts: 2724
Loc: Anaheim, CA. USA
Bjarney has covered it very well!

Just for the sake of redundancy, I'll add some "Simple Stuff":

The Open Delta bank is able to deliver 86.6% of the KVA into 3 Phase loads.

Example: If one pot is 6 KVA and the other is 4 KVA, the output KVA is 8.66 KVA - not 10 KVA. See Bjarney's descriptions and formulas above.

If an existing Closed Delta network (three Pots connected together in a parallel / delta scheme), and one pot fails, the remaining two pots can continue to deliver 3 phase 3 wire AC - but the maximum output KVA is only 58% of the original KVA rating.

Example: 3 - 10 KVA pots connected in a delta scheme has an output power of 30 KVA max.
One pot fails, due to a secondary coil becoming barbequed.
Network can continue to deliver 3 phase 3 wire power, with a maximum of 17.4 KVA apparent power output - as opposed to the original 30 KVA of apparent power available.

The normal rating of a 3 Phase 4 Wire Closed Delta will have a center pot which is at least 200% larger than a single "Outer" pot.

Example: a 45 KVA 3 Phase 4 Wire Closed Delta would have a center pot rated at 25 KVA, and the two "Outer" pots rated at 10 KVA each.

Open Deltas are similar for 4 wire applications, but the "Single Phase" pot might be as large as 400% of the "Kicker" pot. All depends on the calculated loads to be driven.

For 3 Phase 3 Wire settings, the pots are typically sized equally - on both Open and Closed Delta networks.

Scott s.e.t.

P.S. The term "Pot" is referring to a Single Transformer - or more precisely a "Stand-Alone" single phase Transformer.

Bjarney's examples and formulas are much better than my stuff! I'll need to add this to the tech reference section!