The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
12/09/16 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm² flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 9
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 81 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#128241 - 12/02/02 09:54 PM Source Impedance
yu Offline
Junior Member

Registered: 12/03/02
Posts: 1
Loc: na
Hi, needs advice here. What is the different between Line and Source Impedance? A 3-phase x-ray machine is running at 200mA ~ 500mA instead of maximum of 800mA which i suspect is due to cable size. Requirement for X-ray Source impedance is 0.12 ohms. I got the readings on a report as this: RY-0.233, YB-0.239, BR-0.225. Can anybody explain why RY instead of R or Y or B?
tq.

Top
#128242 - 12/03/02 09:32 AM Re: Source Impedance
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
About "...readings on a report as this: RY-0.233, YB-0.239, BR-0.225." What are the units for these numbers? How were these measured or determined?

Top
#128243 - 12/05/02 09:19 AM Re: Source Impedance
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
yu, if I understand correctly, the measured impedance is roughly double what is desired.

Components that most affect impedance are the circuit’s cable size and length, and serving transformer size {impedance.} Each would effect voltage drop on a circuit.

The only solutions I can imagine are 1.) increasing the size or cross-sectional area of the cables, [likely least expensive, but with a potentially limited improvement] 2.) shortening the circuit length [probably not practical] or 3.) installing a larger [lower-impedance/expensive] serving transformer. These three items are probably at least 90% of what effects source impedance on a branch circuit or feeder.

Tests to determine the change {or improvement} from cable replacement may be to carefully apply the instrument at the feeder level if the circuit of interest is indeed a branch circuit, and then at the serving transformer’s secondary terminals.

I hope that answers your question or confirms your suspicions.

Top