P
pauluk Offline OP
Member
Text book explanations don't always make sense. See what you all make of this extract.

From (British publication) The Electrician's Guide to the 16th Edition IEE Wiring Regulations, BS7671, section 5.4.3, sub-sec. 2, Supplementary bonding conductors:

Quote

There will sometimes be doubt if a particular piece of metalwork should be bonded. The answer must always be that bonding will be necessary if there is a danger of severe shock when contact is made between a live system and the metalwork in question. Thus if the resistance between the metalwork and the general mass of earth is low enough to permit the passage of a dangerous shock current, then the metalwork must be bonded.

The question can be resolved by measuring the resistance (Rx) from the metalwork concerned to the main earthing terminal. Using this value in the formula:

Ib = Uo / (Rp + Rx)

will allow calculation of the maximum current likely to pass through the human body where:

Ib is the shock current through the body (A)
Uo is the voltage of the supply (V)
Rp is the resistance of the human body (ohms)
Rx is the measured resistance from the metalwork concerned to the main earthing terminal (ohms).

The resistance of the human body, Rp can in most cases be taken as 1000 ohms although 200 ohms would be a safer value if the metalwork in question can be touched by a person in a bath. Although no hard and fast rules are possible for the value of a safe shock current, Ib, it is probable that 10mA is seldom likely to prove fatal. Using this value with 240V for the supply voltage, Uo, and 1000 ohms as the human body resistance, Rp, the minimum safe value of Rp (sic) calculates to 23k ohms. If the safer values of 5mA for Ib and 200 ohms for Rp are used, the value of Rx would be 47.8k ohms for a 240V supply.

To sum up, when in doubt about the need to bond metalwork, measure its resistance to the main earthing terminal. If this value is 50k ohms or greater, no bonding is necessary. In a situation where a person is not wet, bonding could be ignored where the resistance to the main earthing terminal is as low as 25k ohms.

Looking at the line "when contact is made between a live system and the metalwork in question," my first thought was that this could be interpreted two different ways:

(a) Direct contact between an energized conductor/component and the metalwork, thus energizing that metalwork, OR

(b) Somebody touching an energized circuit/component while being simultaneously in contact with the metalwork.

In case (a) it is obvious that all such metalwork should be bonded to ground to prevent it becoming energized. But the following sentence and the formula which clearly places Rp and Rx in series means that they must be referring to case (b). With me so far? Good!

So, the whole remainder of this section is talking about minimizing the shock risk when somebody simultaneously contacts the exposed metalwork and an enrgized conductor.

They state that if the resistance of the metalwork to ground is over 50K then it doesn't need to be bonded. O.K., so the shock current at 50k (using their own body resistance value of 1k) will be 240V/51k = 4.7mA.

Now let's take a case where Rx is, say, 20k. If left unbonded, the shock current would be 240V/21k = 11.4mA. But by their rules, this metalwork would be bonded to ground, thus reducing the total series resistance to Rp (all but a couple of ohms!) and increasing the current to 240mA.

The rule quoted by this section seems to be saying, in effect: If the shock current with the metal unbonded is under 10mA or so, then we'll leave it at that. But if the shock current would be over 10mA and pose more of a risk, then we'll bond the metal to make sure the sucker gets hit with a full 240mA! [Linked Image]

I'm not arguing for or against bonding here; I'm just saying that the explanation in this section makes no sense.

Anyone????

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Oct 2000
Posts: 5,392
S
Member
Paul,
anything that is not bonded is a potential conductor, the hazards follow any given scenario.
It is interesting that there would be a test or R to the main earthing terminal (MET?) as it would vary......

but..

A lesser 'leak' would likely trip your system there, where the same would take 40X's the umph here to do so....
( enter AFCI's stage left....)
[Linked Image]

Joined: Aug 2001
Posts: 7,520
P
pauluk Offline OP
Member
As I see it, there are two conflicting requirements.

In case (a), where we're looking at the possibility of metalwork becoming energized by some faulty wiring or device, then we would want that metal bonded to ground to open the OCPD or trip the GFI as quickly as possible to prevent it becoming a shock hazard. But the book extract is clearly talking about Rp & Rx being in series, which would not be case in this scenario.

In case (b), where we're concerned with the metal being a return path to ground for somebody touching an energized conductor elsewhere, then bonding that metal to ground will reduce the overall resistance and make the shock more severe. The way the book describes the shock current as V / (Rp + Rx) means that this must be the case they're examining.

Yet they seem to be implying that by bonding the metalwork if the measured resistance is under 50K (or 25K) will reduce the risk, which would be true in the first scenario but not the second.

By the way, this supplementary bonding is in a general section, applicable to armor-grounded, PME, and local ground systems alike (the first two of these will not necessarily have GFI protection).

AFCIs? Oh boy... I'm kinda glad we don't have them over here. Not yet, anyway! [Linked Image]


[This message has been edited by pauluk (edited 06-11-2002).]

Joined: Aug 2001
Posts: 7,520
P
pauluk Offline OP
Member
I finally read through the whole chapter in question and realized exactly what situation this extract is describing.

Yes, they're talking about the metalwork in question as being the return path to ground. However, the source of current is not somebody touching a conductor or part which is energized in normal operation, but rather a supposedly grounded piece of metal which is energized due to a fault.

The case of some appliance is grounded through the cable in the usual way so that a ground fault will open the protective device. But for the length of time it takes that fuse or C/B to open, the casing will be at some potential between 0 and 240V based on fault current times ground circuit resistance.

If the other extraneous metal has a resistance over 50k or so, then the shock current will be negligible. But if that metal has an already low resistance to ground, the p.d. which will exist between it and the case of the faulty device would give rise to a considerable shock current.

So they're saying that by adding a supplementary bond (such as is common in modern bathrooms here) between the exposed metal and the already-grounded appliance case (which is now not at ground potential at all), the fault will raise the voltage on both pieces of metalwork to the same level, thereby ensuring no p.d. between them and therefore no shock. Obviously this supplementary bonding has to be directly to the appliance in question, not back to the main panel where it could make the situation worse.

O.K, I see the logic behind their description now. But we're still left with the problem that if someone does contact some other energized source, bonding that metal more securely to ground will still increase the severity of the shock rsther than reduce it.

You just can't win!

But it does illustrate that bonding can get to be a fairly complex subject.


[This message has been edited by pauluk (edited 06-12-2002).]