#128042 - 05/24/02 12:07 PM why do we parallel conductors?
Eandrew Offline
Member
Registered: 05/24/02
Posts: 68
Loc: seattle, wa, usa
an electrical engineer told me (I'm a fourth year apprentice)that we get more amps per circular mil area with two smaller conductors than one larger conductor each have the same total circular mil area due to heat disapation. in short, the parallel setup, dissapates heat better. But then my forman says that the only reason we do it is for pulling reasons. But if that was true wouldnt you get get bigger pipe/ box etc. Who is correct or more correct?
Top
Tools for Electricians:
#128043 - 05/24/02 12:59 PM Re: why do we parallel conductors?
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Look at the ampacities of the larger cables in Table 310.16. What is the ampacity of 250kcmil? 500kcmil? Does the cable that has twice the area have twice the ampacity?
Don(resqcapt19)
_________________________
Don(resqcapt19)
Top
#128044 - 05/24/02 05:08 PM Re: why do we parallel conductors?
Eandrew Offline
Member
Registered: 05/24/02
Posts: 68
Loc: seattle, wa, usa
well, for a 250kcmil has ampacity of 215 amps
two 250 kcmil in parralel have ampacity of 430 amps.
Now, an equivelant area to two 250 kcmils would be a 500kcmil which has a ampacity of 320amps. A 110 amps less than two parralel 250 kcmil. given in same insulation types.
Top
#128045 - 05/24/02 05:24 PM Re: why do we parallel conductors?
Bjarney Offline
Moderator
Registered: 04/10/02
Posts: 2527
Loc: West-Southern Inner-Northeast ...
I mean no offense, but am surprised that fourth-year training hasn't covered 310-4.
Top
#128046 - 05/24/02 05:54 PM Re: why do we parallel conductors?
maintenanceguy Offline
Member
Registered: 12/02/01
Posts: 300
Loc: Southern NJ, USA
All things that produce heat can only dissipate the heat through their surface. More surface area equals better heat dissipation. Multiple conductors have more surface area than one conductor. And multiple conduits have better heat disipation than one conduit.
Top
#128047 - 05/24/02 07:43 PM Re: why do we parallel conductors?
Eandrew Offline
Member
Registered: 05/24/02
Posts: 68
Loc: seattle, wa, usa
Thank you very much for your responses. I very much like this web site to increase my knowledge. And then pass it on down the road. thanks again
Top
#128048 - 05/24/02 11:46 PM Re: why do we parallel conductors?
Scott35 Offline

Broom Pusher and
Member
Registered: 10/19/00
Posts: 2707
Loc: Anaheim, CA. USA
One other benifit of Paralled Conductors would be a reduction of Skin Effect, which is kind of why two Conductors which total the CM's of a single Conductor can handle more Current.

Scott S.E.T.
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top
#128049 - 06/25/02 05:12 AM Re: why do we parallel conductors?
CECIL Offline
Junior Member
Registered: 12/07/01
Posts: 7
Loc: Runge, tx usa
First, I am not an electrician.

I;'m in HVAC.

My son-in-law bought a new mobile home. THE HOOKUP USE FOUR WIRES.I was told, two hots, one ground and one neutral. Now the neutral and the ground were put under the same lug. Both at the service loop and the distribution box.
HOW CAN THEY BE DEFFERENT, UNDER THE SAME LUG.
I always thought the were derrerent, but maybe not.
What is the derrerence between the ground and the neutral.
Top
#128050 - 06/28/02 10:39 PM Re: why do we parallel conductors?
Scott35 Offline

Broom Pusher and
Member
Registered: 10/19/00
Posts: 2707
Loc: Anaheim, CA. USA
Cecil,

Normally, the Grounded Conductor [AKA the Neutral, or Noodle to be more specific ] would only be Ground Bonded at the main service [we will not include the PoCo's Grounding at the Transformer, since this will complicate things]. If there is a Transformer which the customer has connected on the load side of the main service, the noodle for that system will be grounded at that Xformer only [I'm keeping things simple here!]

Some times a noodle will be re-connected to a grounding electrode system for a sub panel [separate buildings]. This one needs to have only the Earth its self as any conductive path between points of Grounding [Grounding Electrode Systems, or connections between EGCs of the two different panels].

To sum it up, having the noodle ground bonded at the service panel and at a sub panel will cause the Equipment Grounding Conductor to carry some current during normal operation - more than it is supposed to be carrying. This becomes an issue.

If the bonding is done at one universal place / panel, this would be the design intention and be proper Grounding for the noodle.

The point is to not have a parallel ["Neutral"] current flowing in the EGC, or any "Large" amount of current flowing on the EGC during normal operation [Large being something over 1 Amp at the most].

I'm not sure if this explains it well enough for you, so feel free to fire some more Q's this way and most likely another member can pick up the subject and explain it much better to you.

Scott S.E.T.
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top
#128051 - 07/31/02 06:24 AM Re: why do we parallel conductors?
The Watt Doctor Offline
Member
Registered: 12/23/01
Posts: 435
Loc: Mont Belvieu, TX
It can also be less expensive. If you have a chance, look at the price difference between 2" conduit, and 2-1/2". The price is almost double. Copper wire gets expensive in the larger sizes. Then, the labor to install the larger pipe and wire is something else to consider.

Why not parallel?,
Doc
_________________________
The Watt Doctor
Altura Cogen
Channelview, TX
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 52 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals