The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
Is this a fix or just a bandaid?
by gfretwell
10/10/16 06:49 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
renosteinke 6
HotLine1 6
ghost307 5
sparky 4
Who's Online
1 registered (annemarie1), 302 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#127791 - 01/02/02 06:31 AM Cable Ampacities
AF_AimHigh Offline
Junior Member

Registered: 01/02/02
Posts: 2
Loc: Sheppard AFB
Question regarding ampacities for cable. 1999 NEC Table 310-16 basically reflects ampacities of current carrying conductors in raceways, CABLE, etc. Then there Table 400-5 discussing ampacities of cords and CABLE.

Q1: For a #8 AWG conductor, there are differences in ampacities between the two Tables. With no regard to ambient temperature etc. T. 400-5 lists certain types (SJO, STO etc.), while 310-16 lists conductor insulation types (RHW, THW etc.) Given this circumstance, are there two types of "CABLE" available that fall each respectable NEC table?

(I do know there is the new 2002 code but for our writings we only current copyright for 99 code)

Any assistance in this matter would be greatly appreciated.

AF Electrician
Course Developer

#127792 - 01/02/02 06:39 AM Re: Cable Ampacities
Joe Tedesco Offline

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
See Section 240-3. Protection of Conductors
Conductors, other than flexible cords and fixture wires, shall be protected against overcurrent in accordance with their ampacities as specified in Section 310-15, unless otherwise permitted or required in (a) through (g).
Joe Tedesco, NEC Consultant

#127793 - 01/02/02 07:26 AM Re: Cable Ampacities
JBD Offline

Registered: 07/12/01
Posts: 599
Loc: WI, USA
Yes, there are two types of cables.

First are the flexible cord style (i.e. extension cords) these are protected according to NEC99 400-5.
Second are all of the other styles (i.e. NM, and AC) which are protected according to NEC99 310-15.

#127794 - 01/02/02 07:50 AM Re: Cable Ampacities
AF_AimHigh Offline
Junior Member

Registered: 01/02/02
Posts: 2
Loc: Sheppard AFB
Now that clears things up and makes sense! Thanks!