#127786 - 12/20/01 03:44 PM Motion Activated Switch
T, T, Ness Offline
Junior Member
Registered: 03/10/01
Posts: 3
I recently purchased a motion-activated light control switch in the hope that it might be compatible for use with a bathroom exhaust fan, a motor load.

The installation instructions that came with the switch seem to proscribe the intended use with the following:
WARNING: To avoid overheating and possible damage to this device and other equipment, do not install to control a receptacle, motor, or transformer-operated appliance.

The bath exhaust fan is a Broan, Solitaire UltraSilent, model S80U, 1.1 amp

The motion-activated light control switch is a Leviton, model #6791-I for indoor use only, with ratings:
500W-120VAC, 60Hz (Incandescent),
400VA-120VAC, 60Hz, (Fluorescent)

Is there some way to control this fan with the above described switch, or is there another such motion-activated switch available with which would be compatible?

Thanks in advance for helping me solve this riddle.
Top
Tools for Electricians:
#127787 - 12/20/01 05:30 PM Re: Motion Activated Switch
circuit man Offline
Member
Registered: 11/05/01
Posts: 273
Loc: saluda,s.c.
you could proably use a 120v relay. the relay contacts of course would control fan motor & switch would control relay coil. you can pick up such atyour local radio shack or electronics supply house. hope this helps. ERWIN
Top
#127788 - 12/22/01 01:21 PM Re: Motion Activated Switch
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
T,T,Ness,

Leviton has some fairly good tech support;
http://www.leviton.com/sections/techsupp/techindx.htm

I've had good luck with them

Steve
aka sparky
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (Admin), 60 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals