#127620 - 09/05/01 06:26 PM Discussion for: Forward / Reverse motor control  
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,707
Anaheim, CA. USA
Discussion thread for: Forward Reverse AC Motor Control

Feel free to make comments here!!!

Scott SET

P.S. Forgot to complete the subject on the first one [Linked Image]... sorry [Linked Image]

SET


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Tools for Electricians:

#127621 - 09/05/01 06:51 PM Re: Discussion for: Forward / Reverse motor control  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,303
F & R should have an interlock right???


#127622 - 09/05/01 07:12 PM Re: Discussion for: Forward / Reverse motor control  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Scott,
Are people still installing 480 volt control circuits? I haven't seen one installed since I started in trade in '73. I have worked on a few that were installed before I started.
Don(resqcapt19)


Don(resqcapt19)

#127623 - 09/05/01 07:47 PM Re: Discussion for: Forward / Reverse motor control  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,303
well a lot of times there is just no noodle...
[Linked Image]


#127624 - 09/05/01 08:55 PM Re: Discussion for: Forward / Reverse motor control  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Quote
Originally posted by resqcapt19:
Scott,
Are people still installing 480 volt control circuits? I haven't seen one installed since I started in trade in '73. I have worked on a few that were installed before I started.
Don(resqcapt19)


Some self-contained starters with cover mounted controls forego the control transformer. I wouldn't run a 480 control ckt. outside the confines af the starter enclosure.


#127625 - 09/05/01 08:58 PM Re: Discussion for: Forward / Reverse motor control  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Quote
Originally posted by sparky:
F & R should have an interlock right???

sparky,
Do you mean a mechanical interlock? Don't the NC contacts provide electrical interlock?


#127626 - 09/05/01 09:59 PM Re: Discussion for: Forward / Reverse motor control  
Nick  Offline
Member
Joined: Aug 2001
Posts: 599
Riverside, CA
The NC contacts prevent the forward and reverse coils from being energized simultaneously. They don't, however, prevent someone from pressing reverse (or forward) before the motor has stopped turning. [Linked Image]


#127627 - 09/05/01 10:02 PM Re: Discussion for: Forward / Reverse motor control  
spkjpr  Offline
Member
Joined: Dec 2000
Posts: 218
Sedalia,MO, USA
Some starters have a mechanical interlock, most don't. Are we actually talking about an anti-plug circuit to prevent rapid reversal of the motor. Some high speed or heavy loads such as punch presses do use them.


#127628 - 09/06/01 10:11 AM Re: Discussion for: Forward / Reverse motor control  
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
As far as I know all NRTL listed reversing starters come with a mechanical interlock between the F and R contactors. Electrically interlocking the coils is not suffcient to prevent against the creation of a bolted fault.

Scott, the normal convention is to show the contacts of each device next to each other. All of the F power contacts should grouped together rather then intermixed with the R contacs.


#127629 - 09/06/01 08:19 PM Re: Discussion for: Forward / Reverse motor control  
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,707
Anaheim, CA. USA
Hi all, thanks for the comments!!!

I drew these schematics as basic as possible, to keep them as simple as possible.

Only reasons for the 460 VAC input and control circuit were to keep the motor's windings proper [notice how they are series connected, rather than parallel?], and also to show simple control circuitry.

Believe me, I would use a control transformer here!!! Next set of schematics will be more detailed and will include control transformers where applicable.

JBD:Ya, I should have drawn the motor contacts in order - just thought this way would make it easier for people not familiar to motor control circuits. I figured this would better show how the reversal of the Lines is accomplished. Thank you for the heads up! Future drawings will be done more pro!

This schematic shows a crude and basic interlocking control circuit with N.C. contacts for the interlocks in the control circuits for F and R.

This schematic is by no means the best method for this control. It's just to show basics.
Glad that you all made comments about this so others would not begin applying these simple setups to real world applications!!!
I need to remember that when posting schematics on-line, and make note of these facts when posting basic stuff.

Once again, thanks for the comments!!! Hope to have more drawings posted this weekend.

Scott SET


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Page 1 of 2 1 2

Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.024s Queries: 15 (0.004s) Memory: 0.8170 MB (Peak: 0.9920 MB) Zlib enabled. Server Time: 2017-03-28 11:51:13 UTC