#12605 - 08/13/02 05:09 AM Voltage Drop
Frank Cinker Offline
Member
Registered: 07/29/01
Posts: 311
Loc: Pennsylvania
An existing aerial feeder consists of 800 feet of 6AWG and 100 feet of 10AWG. It's 120 volts, single phase. 15amp. load. What is the proper method of determining voltage drop when there are two different size conductors on the same feeder.
I use VD=2KLI/CM
Top
Work Gear for Electricians and the Trades
#12606 - 08/13/02 03:07 PM Re: Voltage Drop
Bob Offline
Member
Registered: 02/05/02
Posts: 182
Loc: Mobile, AL, USA
Use the formula the caculate 800 ft of #6 with 15 amps. Do the same for the #10 at 100 ft with 15 amps and add the two together for the total VD.
Top
#12607 - 08/13/02 03:14 PM Re: Voltage Drop
pauluk Offline
Member
Registered: 08/11/01
Posts: 7520
Loc: Norfolk, England
I'll second that.

Quote:

VD=2KLI/CM


Huh???
Top
#12608 - 08/14/02 03:17 AM Re: Voltage Drop
Frank Cinker Offline
Member
Registered: 07/29/01
Posts: 311
Loc: Pennsylvania
pauluk-

VD= Voltage drop
2= length of circuit x "2"
K= K-factor. 12.9 for copper conductor
L= Length of circuit
I= Amps
CM= Circular mill
Top
#12609 - 08/14/02 04:54 AM Re: Voltage Drop
pauluk Offline
Member
Registered: 08/11/01
Posts: 7520
Loc: Norfolk, England
Thanks. It was getting late and the CM part just didn't register in my mind for some reason (we don't measure in circular mils here).
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
2 registered (gfretwell, sparkyinak), 53 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals