#124679 - 11/30/06 08:54 AM Panel Filler
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Someone recently asked "How expensive can blank filler pieces be?"

In this panel, the white area is all one piece of very sharp-edge aluminum metal siding, cut to fit and mounted to the panel cover with screws.


Top
Tools for Electricians:
#124680 - 11/30/06 10:48 AM Re: Panel Filler
steve ancient apprentice Offline
Member
Registered: 03/04/05
Posts: 169
Loc: west springfield,mass
Two Words: UNBELIVEABLE STUPIDITY
Top
#124681 - 11/30/06 04:34 PM Re: Panel Filler
ShockMe77 Offline
Member
Registered: 06/11/05
Posts: 821
Loc: Rahway, New Jersey
What, no copper siding laying around?
Top
#124682 - 12/01/06 04:31 AM Re: Panel Filler
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
Doesn't the piece of sheet metal do a better job of closing the opening than the filler plates on the other side of the panel do?

(Sharp edges are no good when someone's fumbling around in the dark).
Top
#124683 - 12/01/06 09:25 AM Re: Panel Filler
mamills Offline
Member
Registered: 11/30/01
Posts: 745
Loc: Wharton, Texas, USA
Is the piece of sheet metal secured to the inside of the cover (well secured, I hope)? Those individual metal filler plates always bother me with the way they move around so easily. I'm afraid one is going to fall inside the panel, with possibly disastrous results.

Mike (mamills)
Top
#124684 - 12/01/06 04:45 PM Re: Panel Filler
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Yes, Mike. If you look at the face of the cover, near the edge of the indented portion, you can see the screw heads. These were actually screw / nut fasteners, and not the self-drilling type.
Top
#124685 - 12/01/06 05:24 PM Re: Panel Filler
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
Quote:
"How expensive can blank filler pieces be?"


Those little pieces of injection molded plastic are NOT a bargain at $1.30 each
There's about $30.00 worth (cost) missing out of this load center.
Top
#124686 - 12/02/06 04:07 PM Re: Panel Filler
Scott35 Offline

Broom Pusher and
Member
Registered: 10/19/00
Posts: 2707
Loc: Anaheim, CA. USA
Question(s) about this Panelboard - more as to the System feeding it...

I see something written at the top of the open door (on the back, above the specs sheet / circuit directory), which looks like:

"C Ø High Line"

Is this Panelboard on a 240/120V, 3Ø 4 Wire Delta System?

If so, position "C" is not the "NEC Preferred" location for the "Stinger Phase" - and from the looks of the 1 Pole Breaker(s) in position "C", the connected loads may experience a sudden loss of smoke, if they are rated for 120 VAC maximum.



Just wanted to toss this baloney out for purposes of chewing on it!

Scott35
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top
#124687 - 12/02/06 04:48 PM Re: Panel Filler
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Scott, darn your sharp eyes!

I actually have two pics of the inside of this panel, which is extremely well marked as to the high leg.

This industrial park does, in fact, have a row of units with a "high leg;" that is, 208v to ground, rather than 120. That row also has the high leg at position "C". BUT....

As well marked as the panel is, the markings were not changed when the PoCo upgraded to true three-phase service. I did check, and every leg is 120v to ground .. no high leg after all!
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6775
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 14 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals