#124606 - 11/10/06 08:41 PM Water Damaged Panelboard
Webmaster Offline

Administrator
Member

Registered: 10/07/00
Posts: 3142
Loc: NY, USA
 Quote:
These pictures are from a residence in Bucks County, PA. The owners of the property went on vacation for two weeks, while their basement was filling up with water from a broken pipe. The water rose to the top of the basement ceiling joists.

- HCE727





Top
Tools for Electricians:
#124607 - 11/11/06 04:06 AM Re: Water Damaged Panelboard
TwinCitySparky Offline
Member

Registered: 03/23/06
Posts: 52
Loc: Minnesota
Aaa!

A little scraping with a metal wire brush and she'll be fine.

Top
#124608 - 11/11/06 04:22 AM Re: Water Damaged Panelboard
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
What I find amazing is that nothing in there tripped. They probably ran the sump pumps off electricity from that panel!

Top
#124609 - 11/11/06 06:48 AM Re: Water Damaged Panelboard
Texas_Ranger Offline
Member

Registered: 12/17/01
Posts: 2343
Loc: Vienna, Austria
What does that tell us?
Tap water is often less conductive than you'd think!

Top
#124610 - 11/11/06 07:19 AM Re: Water Damaged Panelboard
Theelectrikid Offline
Member

Registered: 04/30/04
Posts: 854
Loc: Levittown, PA
Wow. Good point Ranger. What township/borough was this in?

Ian A.
_________________________
Is there anyone on board who knows how to fly a plane?

Top
#124611 - 11/11/06 09:57 AM Re: Water Damaged Panelboard
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Less conductive than many think but still plenty of conductivity to deliver a fatal shock.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#124612 - 11/11/06 10:55 AM Re: Water Damaged Panelboard
Elviscat Offline
Member

Registered: 08/13/05
Posts: 214
Loc: Seattle Washington USA
man, those service conductors are freakin' DUST, that thing looks like it was just pulled up from the Titanic!

Top
#124613 - 11/11/06 11:49 AM Re: Water Damaged Panelboard
BigJohn Offline
Member

Registered: 03/06/04
Posts: 352
Loc: Boston, MA
Electrolysis at work, baby! Look at that neutral.

I'm still amazed that nothing tripped, that water would have needed an impedence of better than sixteen ohms to avoid tripping out a 15A breaker on a leg-to-leg fault. Given all the contaminants that I'm sure were floating around in it, I'm amazed it was that resistive.

Maybe the water itself kept the breakers from operating? The cooling would mess up the thermal characteristics and the water itself would foul the mechanism?

On a side note, can you imagine coming home and opening your basement door to find water lapping at the top step? That must've been horrifying.

-John

Top
#124614 - 11/11/06 04:57 PM Re: Water Damaged Panelboard
HCE727 Offline
Member

Registered: 11/11/05
Posts: 190
Loc: Delaware County, PA, USA
'Kid, this is in Bensalem.
_________________________
Hank

Top
#124615 - 11/12/06 03:12 AM Re: Water Damaged Panelboard
Texas_Ranger Offline
Member

Registered: 12/17/01
Posts: 2343
Loc: Vienna, Austria
 Quote:
On a side note, can you imagine coming home and opening your basement door to find water lapping at the top step? That must've been horrifying

To some extent I can... About 1 1/2 years ago I came home to a sound of heavily running water. When I went down into the dark basement fumbling for the light switch I thought: "What's that weird feeling around my shoes???" Looked down to realize I was wading in almost 2 inches of water...

Some ingenious kid had turned on the sink at full blast, filling it with more water than the drain could take... go figure. Took three of us more than half an hour with buckets and shovels.

Top