The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Safety at heights?
by Trumpy
27 minutes 52 seconds ago
Old Bath Fan
by gfretwell
Today at 01:38 AM
Search Function
by Webmaster
Yesterday at 11:13 PM
Forum Software Upgrade coming soon...
by Webmaster
Yesterday at 09:17 PM
ESA Arc flash course
by frank
Yesterday at 04:25 PM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Webmaster 30
HotLine1 21
Ruben Rocha 16
gfretwell 13
ghost307 12
Who's Online
1 registered (Trumpy), 0 Guests and 167 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#12426 - 08/09/02 06:09 AM 2 pole gfib's
ken m Offline
Member

Registered: 08/14/01
Posts: 61
Loc: south carolina
this question may sound elementary to some but in the installation of a 2-pole gfi breaker for a 240v pump motor what wire connects to the center term (neutral) on the load side of the bkr when there are only 2 ungrounded conductors and 1 equipt grounding conductor? this application is for a swimming pool skimmer pump. is the pump gfi protected?
thx., ken m

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#12427 - 08/09/02 07:54 AM Re: 2 pole gfib's
caselec Offline
Member

Registered: 04/14/02
Posts: 557
Loc: San Jose, CA
If the circuit does not need a neutral then you don't need to run one. If it does need a neutral then it must be connected to the neutral terminal of the GFI breaker. The pump is protected.

[This message has been edited by caselec (edited 08-09-2002).]
_________________________
Curt Swartz

Top
#12428 - 08/09/02 07:58 AM Re: 2 pole gfib's
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Ken,
If the circuit doesn't require a grounded conductor, then there is no connection made to the laod side neutral on the GFCI. The line side neutral must be connected to the panel neutral buss. The GFCI will work just fine on this two wire circuit. It monitiors the current on the two hots and the neutral, and as long as this sums to 0 there is no ground fault. When some of the current returns by a path other than the two hots in your two wire circuit, the sum will no longer be 0. The GFCI will trip when this sum exceeds 4 to 6mA. The same thing happens on a three wire circuit. Under normal conditions, the sum of the three currents is 0.
Don
_________________________
Don(resqcapt19)

Top
#12429 - 08/09/02 01:14 PM Re: 2 pole gfib's
ken m Offline
Member

Registered: 08/14/01
Posts: 61
Loc: south carolina
thanks for the replies! as you can probably sumise i do little to no work on spas and pools. such a liability especially when you know children are in the pool. the reason i was called in to do(correct) the job was the installer had tied the filter(1/2hp) and skimmer pump(1/3hp) motors together on the same 2-pole gfcb (30A). he had the under water pool light(120V) entering the brkr box with the grounded conductor connected to the center post of the 2-pole gfcb. the ungrounded conductor traveled to a remote switch which was then fed from a gfi recpt mounted adjecent to the brkr panel. the pool cover motor was also protected by the same gfi recpt. ????
any comments?