#124171 - 08/20/06 04:50 AM Oddball Fuses
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
Rewired has been exploring again


 Quote:
I happened to stumble on this in the girlfriends apartment building(s).
The " 550" and " 575" amp fuses are in the main disconnect of two of the buildings, the " 380" amp fuses are in a third building which actually has TWO main services, one for the units, one (225 amp main breaker) for the house load and now disconnected electric hot water tanks. ( all had electric hot water at one time, only the other buildings brought in a 100A gooV 3 phase service for the tanks, all of which is now disconnected..

I found a couple good violations that I will post later
















Top
Tools for Electricians:
#124172 - 08/20/06 08:02 PM Re: Oddball Fuses
napervillesoundtech Offline
Member

Registered: 02/28/06
Posts: 144
Loc: Naperville, IL, USA
Individual runs of copper water pipe? That's crazy!

Those also look like custom made fuses. It looks like the ratings were probably hand stamped on them. Those are pretty cool, so long as theyre used properly

Top
#124173 - 08/20/06 08:40 PM Re: Oddball Fuses
mxslick Offline
Member

Registered: 10/24/04
Posts: 785
Loc: Atomic City, ID USA
Don't think that's water pipe, but a metal-encased, mineral powder filled (as insulation) cable. I forget the tradename, but there was a thread about it on here somewhere....
_________________________
Stupid should be painful.

Top
#124174 - 08/20/06 10:09 PM Re: Oddball Fuses
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Pyrotenax.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#124175 - 08/21/06 04:16 AM Re: Oddball Fuses
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
In the NEC it is called MI Cable.

It is fireproof (more or less) it can operate even while sections of it are exposed to open flame.

A typical use of it is for life safety emergency circuits.

The insulation between the copper conductor and the copper sheath looks like Sheetrock and is somewhat flexible until exposed to high heat than I believe it turns hard more like ceramic.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#124176 - 08/21/06 12:12 PM Re: Oddball Fuses
RODALCO Offline
Member

Registered: 12/08/05
Posts: 863
Loc: Titirangi, Akld, New Zealand
or MIMS

Mineral Insulated Metal Sheethed
_________________________
The product of rotation, excitation and flux produces electricty.

Top
#124177 - 08/21/06 02:43 PM Re: Oddball Fuses
Rewired Offline
Member

Registered: 01/01/06
Posts: 567
Loc: Hamilton, Ontario, Canada
Just an off the wall question but do you think they used this type of conductor because it basically runs unfused from the service head ( between the 2nd and 3rd floors) down to the sub basement where the disconnect is located... I assume they would have to have buried it in the masonry and concrete slab for protection?!?!
Doesnt seem correct, but thats how it was done 40+ odd years ago.

A.D

Top
#124178 - 08/21/06 05:42 PM Re: Oddball Fuses
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Here is the thread where MI (pyro) cable was discussed.

{Message edited to fix tag}

[This message has been edited by Trumpy (edited 08-21-2006).]
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#124179 - 08/21/06 08:27 PM Re: Oddball Fuses
Rewired Offline
Member

Registered: 01/01/06
Posts: 567
Loc: Hamilton, Ontario, Canada
Very cool! I will be definately looking up more information on pyro cables. That is the first time I have actually seen it installed and in service. Too bad its not too popular here any more, I would have really liked to get lessons on how to properly install pyro and get some hands on experience installing the stuff.

A.D

Top
#124180 - 08/22/06 04:32 AM Re: Oddball Fuses
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
It looks like the lock nuts on the MI connectors are ferrous. That could be a problem. It apprears that the 3 MI connectors enter the enclosure via some type of plate that is bolted to the inside of the enclosure. I assume that is nonferrous to pevent induction heating.
Don
_________________________
Don(resqcapt19)

Top