#122882 - 01/29/06 04:41 PM Bad CT Cabinet
Webmaster Offline

Administrator
Member

Registered: 10/07/00
Posts: 3142
Loc: NY, USA
 Quote:
Hi, I am an Electrician in Roanoke Virginia. I have a 3 Phase 120/208 system in a building I am working on for my company. Our local Power Company subbed out another company to wire their end of the CTs. It has taken them 5 days to get this far, but I am glad they did not energize it. This is a 1600 Amp Service - my work on top, Power Company coming in on bottom. This is just unbelievable.

When the sub was confronted about what he had done he really thought he did nothing wrong and even said this is how he was taught to do it in West Virginia.

Look closely at his neutrals, and what you can't see is that in the Xfmr each pipe full of wire is made to a phase so you see B,O,Y,N in a ring here it is all made to A, or B, or C in the Xfmr. I just could not believe it.

The Power Company who had hired them made them fix it and I made them ring out the wires to make sure everything was the way it needed to be, but the guy really did not know what he was doing and as for the Power Company, they are going to question what terminations have been made all over and under the city. This guy was the lead termination guy for his crew and has done a lot of work for our Power Company.

- (no name given)


[This message has been edited by Webmaster (edited 01-29-2006).]

Top
Tools for Electricians:
#122883 - 01/29/06 05:18 PM Re: Bad CT Cabinet
JAKEE Offline
Junior Member

Registered: 01/29/06
Posts: 4
Loc: Hardy,Va.USA
Sorry about the no name. I want to make a correction. That company has done alot of work for the local power company not just the crew doing this work.

Top
#122884 - 01/29/06 06:14 PM Re: Bad CT Cabinet
Dnkldorf Offline
Member

Registered: 12/12/04
Posts: 1091
Loc: nowhere usa
(jaw hanging down in disbelief)


Unbelieveable.....


Dnk..

Top
#122885 - 01/29/06 06:26 PM Re: Bad CT Cabinet
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
What Dnk said!!!

Jakee, welcome to the forum.

Roger

Top
#122886 - 01/29/06 06:34 PM Re: Bad CT Cabinet
BigJohn Offline
Member

Registered: 03/06/04
Posts: 352
Loc: Boston, MA
Let me see if I understand this:

Each pipe containes parallels for a single phase? I.e.: first pipe, A phase. Second pipe, B phase, etc.?

And the guy terminating the cables through the CTs basically created a bunch of dead-short-circuits by connecting one cable from each phase to the same bus?

But here's the trick: Why in the world did whoever installed the cables run a neutral with each pipe? If I was the guy terminating this job, I might just as soon see that and think that each pipe was supposed to contain all three phases plus a neutral. Or were the cables and terminations all done by the same fellow?

-John

Top
#122887 - 01/29/06 06:40 PM Re: Bad CT Cabinet
frenchelectrican Offline

Member

Registered: 02/06/03
Posts: 938
Loc: Wi/ Paris France { France for ...
the other thing the POCO did goof up major time if you look at the CT doughnuts and the wire colors if reading for metering why they go all 3 phase for each CT that will cancled the current reading very effective.

the only way to get the correct reading on CT is have each phase for CT doughnuts that way the meter will read it correct.
i am suprised how they do that

Merci. Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


Top
#122888 - 01/29/06 07:09 PM Re: Bad CT Cabinet
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
Cute how our man jumps from high voltage colors to low voltage colors...and NO XFMR....

This priceless photo is so hairball....

It belongs forever in the ECN archive.
_________________________
Tesla

Top
#122889 - 01/29/06 07:13 PM Re: Bad CT Cabinet
mahlere Offline
Member

Registered: 11/17/05
Posts: 514
Loc: New Jersey
what kind of conduits coming in from the xfrmr? look to be rigid. Didn't think you could separate the phases in metal conduits.

Top
#122890 - 01/29/06 08:20 PM Re: Bad CT Cabinet
Radar Offline
Member

Registered: 04/30/04
Posts: 349
Loc: Los Angeles, CA
 Quote:
why they go all 3 phase for each CT that will cancled the current reading very effective


That would be OK with me, if I were paying the power bill.
_________________________
There are 10 types of people. Those who know binary, and those who don't.

Top
#122891 - 01/29/06 08:24 PM Re: Bad CT Cabinet
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
If there are an AØ, a BØ, and a CØ in each of those incoming conduits, I've got some customers that would just love to have this guy hook up their services.