electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
300.5 (D)(3) Requires a warning ribbon at least a foot above unencased service conductors that are buried more than 18" deep.
Don't you think that this should be required on other underground installations as well?


Top
Tools for Electricians:
#122583 - 12/02/05 08:08 PM Re: Scope of 300.5 (D) (3)
skingusmc Offline
Member
Registered: 05/27/04
Posts: 116
Loc: Simi Valley, CA USA
You mean this isn't a "warning" to AHJs? (grin)

Steve
_________________________
Thanks
Steve
Top
#122584 - 12/03/05 01:08 AM Re: Scope of 300.5 (D) (3)
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
Scott,
Did you get that strip from the local cemetary?.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top
#122585 - 12/03/05 01:33 PM Re: Scope of 300.5 (D) (3)
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
I think the proper cite(s) would be 90.2 and 90.4.
(Especially in regards to enforcing non-existant requirements or the use of no-existant equipment).
Top
#122586 - 12/03/05 04:58 PM Re: Scope of 300.5 (D) (3)
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
Upon finding this tape in the ground do you hand dig, or continue with a back-hoe?
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#122587 - 12/05/05 04:53 PM Re: Scope of 300.5 (D) (3)
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
OK, maybe the example is a little silly, but I think my question is a valid one.

Why should it be a requirement to put a warning ribbon above a 100 Amp residential 120/240 Volt service lateral, maybe fed by a 25 KVA transformer, when there's no requirement to provide the same type of warning above a 1000 Amp 480 Volt feeder?

Is my reasoning even goofier than usual? What am I missing here?
Top
#122588 - 12/05/05 05:24 PM Re: Scope of 300.5 (D) (3)
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
IMO your right, it makes no sense to me that this only applies to service conductors.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#122589 - 12/05/05 05:28 PM Re: Scope of 300.5 (D) (3)
HLCbuild Offline
Member
Registered: 12/05/04
Posts: 209
Loc: Herndon,Va USA
You guys are thinking too much again!
Top
#122590 - 12/06/05 06:37 AM Re: Scope of 300.5 (D) (3)
sandsnow Offline
Member
Registered: 09/21/04
Posts: 167
Loc: Irvine, CA, USA
Scott
Read 300.5(D) It is refering to direct buried conductors and cables. This does not apply to service conductors or laterals in conduit.

I've never heard of any direct buried cables encased in concrete though.

I agree that UG conductors in general need more attention from the code in regards to protection.
_________________________
Larry LeVoir
Inspector
City of Irvine, CA
Top
#122591 - 12/06/05 10:54 AM Re: Scope of 300.5 (D) (3)
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
It also doesn't make any sense that this only applies to condutors installed in a trench, not those installed by directional boring.
Don
_________________________
Don(resqcapt19)
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 36 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals