#121709 - 08/13/05 07:05 PM Meter Ring Failure
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
Pictures and info submitted by Renosteinke:
Quote:
When the PoCo went to disconnect service for non-payment, the meter ring came apart, leading to a service fault to ground.

The meter base was probably made just before WWII. Manufactured by Square D, the box cover had little slots, into which tabs on the ring were press-fit. Unfortunately, the meter socket was also attached to the ring- so when the ring came forward with the meter, the socket also cam forward, contacting the box.

At about 2 O'clock on the cover, you can see a round notch in the cover, caused by this arc.

Farther down the line, you can see the scorch mark on the EMT, caused by this fault arcing between the two pieces of EMT.

Best I can tell the meter-puller had to stand there, in the winter cold, confronted by hostile non-English speaking tenants, holding the meter in place- while waiting for assistance to come, and disconnect power at the pole!

Then I got to do a service change!




_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top
Tools for Electricians:
#121710 - 08/16/05 12:46 AM Re: Meter Ring Failure
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
John, is it the light or is that really EMT?.
I thought it must have been some sort of Romex cable?.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top
#121711 - 08/16/05 07:34 AM Re: Meter Ring Failure
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
The silver piece is EMT; the vertical "white" pipes are RMC.
Top
#121712 - 08/16/05 01:31 PM Re: Meter Ring Failure
mxslick Offline
Member
Registered: 10/24/04
Posts: 803
Loc: Atomic City, ID USA
Had a similar failure some years ago doing a service change working for EC here in So. Cal.

The cross piece holding the LINE side clips broke free while I was pulling the meter. The explosion shot the meter across the yard. Despite the fact that I was very stupidly not wearing proper PPE (just sunglasses and a t-shirt) all I got was a huge scare and ringing ears.

I climbed the ladder, cut the drop and removed that panel with a 20lb sledgehammer! The meter met the same fate. (Luckily for me, the POCO was going to upgrade the meter anyway. They laughed when I told them what happened.)

I'll be back with an edit of this post, to put up a link to a device designed to help safely pull and install meters. Don't touch that dial!

Edit: Here's the link to the product:
http://www.rauckmanutility.com/products.htm

Click on either pic of "Meter Puller"



[This message has been edited by mxslick (edited 08-16-2005).]
_________________________
Stupid should be painful.
Top
#121713 - 08/17/05 08:44 AM Re: Meter Ring Failure
houleelect Offline
Junior Member
Registered: 07/19/05
Posts: 4
Loc: Ypsilanti, MI USA
It looks like EMT was bent without aid of bender. Not a bad job for no bender.
_________________________
Larry Houle
Top
#121714 - 08/18/05 08:54 PM Re: Meter Ring Failure
yaktx Offline
Member
Registered: 02/19/03
Posts: 288
Loc: Austin, Texas, USA
Anytime I come across a metercan that old (my utility has used ringless since the mid-60s), I climb a ladder and cut the drop before messing with it. If I'm not there to change the service, I don't mess with it. Ones I have opened are just too scary!
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 55 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals