#121553 - 07/22/05 08:29 PM Incorrect Lugs Used
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Photo submitted by D Thomas
 Quote:
The attached photo is a hot joint on a 3phase motor isolator, the reason for the failure is that an incorrect lug (copper) was used to terminate an aluminium cable. As you can see in the photo the other two lugs under the tape are much larger, these are bi-metallic lugs.




Thanks mate.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
Tools for Electricians:
#121554 - 07/24/05 04:31 PM Re: Incorrect Lugs Used
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
I was recently reading an article on Crimp Lugs used in electrical installations and apparently this particular problem is the most common cause of cable/connector failure, next to using the wrong sized connector.
Looks like this particular crimp lug has just corroded and burned away because of the higher resistance connection.
This could have been a nasty failure had it gone un-noticed.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#121555 - 01/19/06 02:54 AM Re: Incorrect Lugs Used
RODALCO Offline
Member

Registered: 12/08/05
Posts: 863
Loc: Titirangi, Akld, New Zealand
It requires the isolator to be replaced and white Ø cable extended and re terminated to new islolator switch to remedie this fault properly.

Same here too the Al cable needs enough surface area in the lug to have a low resistance connection between cable and lug

I have found it here many times too in distribution pillars and transformers.
Wrong lugs used to terminate to busbar or NZI fuses in transformers. or Cu droppers made to connect bimettalic lugs to and not enough surface area between lug and dropper causing hot spots.

The bimetalic lugs also rely on the surface area between lug and terminal to allowe for a low resistance surface hence the larger size of the eye.

Seen many times that solid Al 70 mm² cables just been srewed straight into HRC fuse carriers without any transition joint or joint compound used.
_________________________
The product of rotation, excitation and flux produces electricty.

Top
#121556 - 01/25/06 02:19 AM Re: Incorrect Lugs Used
kiwi Offline
Member

Registered: 12/04/04
Posts: 347
Loc: christchurch new zealand
Cool Photos ! I've often wondered what that would look like when it fails. Ali cable in a copper lug. Who'd do that ?

Top