The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 198 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#12152 - 08/01/02 05:47 AM Sansui "Split unit" AC
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
I was asked to wire an AC unit that comes supplied with plasticized flexible cords to bring power from the disco. to the condensing unit, and from the condenser to the (thru-the-wall) evaporator.
The connection from the condenser reqiures 4 conductors. The manufacturer used a 3 conductor cord and one wire from a 2 conductor cord and taped them together. Due to the design of the equipment, sealtite could not be easily adapted to these units. This means that the cords have no physical protection. The manufactures states that the supplied wiring must be used. (I guess it's a warranty thing).
Anyone ever deal with this sort of equipment?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#12153 - 08/01/02 03:54 PM Re: Sansui "Split unit" AC
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Redsy:
We have wired quite a few of this type unit, and I have not seen any with cords/factory wiring as you explained.
Sanyo and Carrier are the brands out here.
Sealtite and EMT between the Cu and the fan/coil units. (4 wires)

BTW; anyone have any input as to a disco required/needed at the interior unit???
(Fan.Coil)

HotLine1
John
_________________________
John

Top
#12154 - 08/01/02 03:55 PM Re: Sansui "Split unit" AC
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Redsy:
We have wired quite a few of this type unit, and I have not seen any with cords/factory wiring as you explained.
Sanyo and Carrier are the brands out here.
Sealtite and EMT between the Cu and the fan/coil units. (4 wires)

BTW; anyone have any input as to a disco required/needed at the interior unit???
(Fan.Coil)

HotLine1
John
_________________________
John

Top
#12155 - 08/03/02 05:20 AM Re: Sansui "Split unit" AC
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
I had a similar unit to connect last year,& although not a Sansui, it was Japanese made.
Some clown A/C co. had installed it in a small server room
115(yes)volt, it had no NRTL label, and the diagrams supplied showed the grounded conductor being switched. 4 wires (@ full voltage) ran from the condenser to the evaporator.
The unit never worked well, and I had 4 callbacks (none of which were problems with my wiring) when it failed repeatedly, one time nearly cooking about $100K in equipment.
I'd never hook up another one of these pieces of junk...S