#121377 - 07/08/05 08:18 PM Fire Sprinklers and Electrical Equipment  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,259
Fullerton, CA USA
Quote
This install made me wonder....Do we really want it to be possible for a sprinkler head to spray directly into the open sides of bus-duct?



renosteinke


[Linked Image]


Tools for Electricians:

#121378 - 07/08/05 09:36 PM Re: Fire Sprinklers and Electrical Equipment  
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
Emormous shunt trip CB connected to flow switch?


Mark Heller
"Well - I oughta....." -Jackie Gleason

#121379 - 07/09/05 11:44 AM Re: Fire Sprinklers and Electrical Equipment  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
The disconnects serve assortes electrical panels located directly underneath. This is actually the main service for an older shopping center

As a side note, this place has been remodeled and expanded so many times that the panel directories contain numerous "identifications" as "Unknown" and "if anyone knows what this is for, please let maintenance know."


#121380 - 07/09/05 12:43 PM Re: Fire Sprinklers and Electrical Equipment  
rad74ss  Offline
Member
Joined: Apr 2004
Posts: 156
Pryor, OK USA
I would have thought that Halon or CO2 would have been required there.

Personally I would have set aside some maintenance time so that the buss could be deenergized and that sprinkler head capped.

Scenario: Electrical fire in the fry-daddy aisle, sprinklers go off.

Supervisor; "Johnny go turn off the electrical power, it's by the wall over there."

Now there are two fry-daddy aisles with electrical fires in them.


#121381 - 07/09/05 03:45 PM Re: Fire Sprinklers and Electrical Equipment  
BigJohn  Offline
Member
Joined: Mar 2004
Posts: 391
Boston, MA
What's the average activation temperature of these sprinkler heads? I was under the impression that the fusible link/glass bulb in most heads wouldn't fail unless the fire was just about directly under them. That is, they needed a whole lot of heat. If it gets to that point, isn't that bus duct already gonna be compromised?

-John


#121382 - 07/09/05 05:22 PM Re: Fire Sprinklers and Electrical Equipment  
bensonelectric  Offline
Member
Joined: Mar 2005
Posts: 12
Portland OR United States
I have seen a glass-bulb type trigger point as low as 155 F.


#121383 - 07/10/05 01:30 AM Re: Fire Sprinklers and Electrical Equipment  
Big Jim  Offline
Member
Joined: Jul 2003
Posts: 394
Denver, CO USA
Ceiling temperatures skyrocket rapidly in the event of a fire. I've seen demonstrations where they were over several hundred degrees in minutes. Unless there was a large amount of ventilation in that room, the sprinkler would soon go off in the event of any real fire.


#121384 - 07/10/05 09:05 AM Re: Fire Sprinklers and Electrical Equipment  
dmattox  Offline
Member
Joined: Oct 2004
Posts: 265
Anaheim, CA
Don't know about old buildings, but the ones we do with backflows and PIVs are designed so that when the fire department shows up they select the building on fire and pressurize it up to 200 PSI. This results in all the sprinkler heads in the building going off. They might get a nice secondary explosion here =\

Though they are supposed to turn off the main when they show up, just don’t know if they do it before or after they set off the whole sprinkler system.


#121385 - 07/10/05 09:45 AM Re: Fire Sprinklers and Electrical Equipment  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Quote
but the ones we do with backflows and PIVs are designed so that when the fire department shows up they select the building on fire and pressurize it up to 200 PSI. This results in all the sprinkler heads in the building going off


I am sorry I really have to question that, I think you may have been given incorrect info or misunderstood the info.

That is what happens in the movies, I have worked a lot of commercial buildings and have never seen a sprinkler system operate in that way.

The FD may very well turn on fire pumps but I doubt highly that causes all sprinkler heads to let go.

Two problems with that.

1)You would be basically 'wasting' your water supply and your main would have to be sized to run all heads at the same time.

I doubt a sprinkler main can support all heads open any more than our service main can handle all circuits fully loaded.

2)Insurance Companies. As much as the insurance company wants the fire out they definitely do not want water damage in the entire building for a localized fire.


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#121386 - 07/10/05 12:01 PM Re: Fire Sprinklers and Electrical Equipment  
dmattox  Offline
Member
Joined: Oct 2004
Posts: 265
Anaheim, CA
I've never seen em do that in the movies, this is how I've been told they do it by the sprinkler guys.

I do a lot of multi building tilt ups. There is a main sprinkler line that goes onto the property to the backflow, from there it splits off to a PIV (Post indicator valve) for each building. What I have been told is that when the fire department shows up, they shut off the PIVs to all other buildings on the property and then hook their engine up to the system. The backflow prevents the pressure from going back to the main feed off the property. This then results in the heads of the buildings going off.

From what I have been told, the fire department's lowest priority are the contents of the building. Saving lives, preventing spread to other buildings is their primary concern, followed by saving the structure currently on fire.

As I am sure you have seen, even one sprinkler head going off can basically destroy the contents of a small-medium size building. Let alone what the smoke and fire will do.

I am sure other buildings are different, but this is how I've been told it works for tiltups.


Page 1 of 3 1 2 3

Member Spotlight
sparky66wv
sparky66wv
West Virginia
Posts: 2,232
Joined: November 2000
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.024s Queries: 15 (0.005s) Memory: 0.8192 MB (Peak: 0.9979 MB) Zlib enabled. Server Time: 2017-03-23 20:08:02 UTC