#121179 - 06/21/05 05:28 PM Floor Outlets
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
These are in a new commercial kitchen under a peninsular food prep counter. What do you suppose the installer was thinking?

Submitted by Lostazhell





Top
Tools for Electricians:
#121180 - 06/21/05 06:09 PM Re: Floor Outlets
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
OK- so he didn't use a 'real' floor box! Let's at least give the guy credit for having his heart in the right place; there is a gasket, the cover will keep stuff from dripping in, and -if all are placed like this one- they are out of the way of foot trafic.
Not that I expect the covers to last very long!

Even a rated floor box would allow stuff to drip inside, and surely wouldn't keep mopwater out whereever there was a plug inserted. I think this application would be better served by "tombstone" pedestals for stuff under the counters, and drop cords for everything else.

As nice, reliable, and prooven GFCI's are, they are no substitute for good design.
Top
#121181 - 06/21/05 06:10 PM Re: Floor Outlets
Alan Nadon Offline
Member
Registered: 03/10/05
Posts: 399
Loc: Elkhart, IN. USA
What do I think he was thinking ? He wasn't !
He obviously has never worked in a kitchen when it is washdown time.
Alan.
_________________________
Alan--
If it was easy, anyone could do it.
Top
#121182 - 06/21/05 06:13 PM Re: Floor Outlets
techie Offline
Member
Registered: 05/17/05
Posts: 246
Loc: palo alto, ca usa
I bet he was thinking "damn architects.. how the ****** am I supposed to do this, and keep the outlets dry when they mop the floor?"

Personally, I would have brought the outlets down from above on pendants, and kept the floor clear.

I don't think that brass floor plates would work well here, A/V style floor pockets would collect water and crud, and the office style speed bumps would probably have the same problem, with no protection.
The other option might be to mount a piece of strut, and mount the outlets above the floor level, fed with LT from below.

(edited to remove "misspelled" profanity)



[This message has been edited by electure (edited 06-22-2005).]
Top
#121183 - 06/22/05 02:32 AM Re: Floor Outlets
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Quote:
I bet he was thinking "damn architects.. how the #@^% am I supposed to do this, and keep the outlets dry when they mop the floor?"


I second that thought.

I doubt an electrician decided that spot needed floor outlets.

At least they are GFCI.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#121184 - 06/22/05 04:32 AM Re: Floor Outlets
IanR Offline
Member
Registered: 12/06/04
Posts: 328
Loc: Palm Bay FL USA
Personally I would hope that a GFCI CB feeds these outlets. A wash down would most likely drip on the unprotected (line) side of those GFIs. IMHO putting any recepts on the floor in a washdown area like that is like playing Russian Ruelette. Pendants from the ceiling would have been my choice.
Top
#121185 - 06/22/05 04:41 AM Re: Floor Outlets
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
Quote:
In this government building, the floor is liberally sprinkled with receptacles like this one. Cut-in box, device- and cover suspended above it all by the carpet and padding. What was that rule about space between the box and flammable materials? Figure there's a 1/4 inch gap at each one. Oh, and wouldn't you like to be the carpet cleaner?
At least, with a receptacle under each cluster of desks, they weren't using extension cords.


Renosteinke


Top
#121186 - 06/22/05 12:15 PM Re: Floor Outlets
wa2ise Offline
Member
Registered: 11/29/02
Posts: 782
Loc: Oradell NJ USA
That government building office wasn't the electrical inspector's, was it?
Top
#121187 - 06/22/05 06:12 PM Re: Floor Outlets
Lostazhell Offline
Member
Registered: 02/21/04
Posts: 1428
Loc: Bakersfield, CA (Originally Or...
FYI.... The prints called for cord drops which is what they have now...
Top
#121188 - 06/22/05 06:43 PM Re: Floor Outlets
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
So Randy, what do the boxes on the floor have now?
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 45 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals