#121179 - 06/21/05 08:28 PM Floor Outlets  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,259
Fullerton, CA USA
These are in a new commercial kitchen under a peninsular food prep counter. What do you suppose the installer was thinking?

Submitted by Lostazhell


[Linked Image]


[Linked Image]


Tools for Electricians:

#121180 - 06/21/05 09:09 PM Re: Floor Outlets  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
OK- so he didn't use a 'real' floor box! Let's at least give the guy credit for having his heart in the right place; there is a gasket, the cover will keep stuff from dripping in, and -if all are placed like this one- they are out of the way of foot trafic.
Not that I expect the covers to last very long!

Even a rated floor box would allow stuff to drip inside, and surely wouldn't keep mopwater out whereever there was a plug inserted. I think this application would be better served by "tombstone" pedestals for stuff under the counters, and drop cords for everything else.

As nice, reliable, and prooven GFCI's are, they are no substitute for good design.


#121181 - 06/21/05 09:10 PM Re: Floor Outlets  
Alan Nadon  Offline
Member
Joined: Mar 2005
Posts: 399
Elkhart, IN. USA
What do I think he was thinking ? He wasn't !
He obviously has never worked in a kitchen when it is washdown time.
Alan.


Alan--
If it was easy, anyone could do it.

#121182 - 06/21/05 09:13 PM Re: Floor Outlets  
techie  Offline
Member
Joined: May 2005
Posts: 246
palo alto, ca usa
I bet he was thinking "damn architects.. how the ****** am I supposed to do this, and keep the outlets dry when they mop the floor?"

Personally, I would have brought the outlets down from above on pendants, and kept the floor clear.

I don't think that brass floor plates would work well here, A/V style floor pockets would collect water and crud, and the office style speed bumps would probably have the same problem, with no protection.
The other option might be to mount a piece of strut, and mount the outlets above the floor level, fed with LT from below.

(edited to remove "misspelled" profanity)



[This message has been edited by electure (edited 06-22-2005).]


#121183 - 06/22/05 05:32 AM Re: Floor Outlets  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Quote
I bet he was thinking "damn architects.. how the #@^% am I supposed to do this, and keep the outlets dry when they mop the floor?"


I second that thought.

I doubt an electrician decided that spot needed floor outlets.

At least they are GFCI. [Linked Image]


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#121184 - 06/22/05 07:32 AM Re: Floor Outlets  
IanR  Offline
Member
Joined: Dec 2004
Posts: 328
Palm Bay FL USA
Personally I would hope that a GFCI CB feeds these outlets. A wash down would most likely drip on the unprotected (line) side of those GFIs. IMHO putting any recepts on the floor in a washdown area like that is like playing Russian Ruelette. Pendants from the ceiling would have been my choice.


#121185 - 06/22/05 07:41 AM Re: Floor Outlets  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,259
Fullerton, CA USA
Quote
In this government building, the floor is liberally sprinkled with receptacles like this one. Cut-in box, device- and cover suspended above it all by the carpet and padding. What was that rule about space between the box and flammable materials? Figure there's a 1/4 inch gap at each one. Oh, and wouldn't you like to be the carpet cleaner?
At least, with a receptacle under each cluster of desks, they weren't using extension cords.


Renosteinke


[Linked Image]


#121186 - 06/22/05 03:15 PM Re: Floor Outlets  
wa2ise  Offline
Member
Joined: Nov 2002
Posts: 782
Oradell NJ USA
That government building office wasn't the electrical inspector's, was it? [Linked Image]


#121187 - 06/22/05 09:12 PM Re: Floor Outlets  
Lostazhell  Offline
Member
Joined: Feb 2004
Posts: 1,428
Bakersfield, CA (Originally Or...
FYI.... The prints called for cord drops [Linked Image] which is what they have now...


#121188 - 06/22/05 09:43 PM Re: Floor Outlets  
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
So Randy, what do the boxes on the floor have now?


Mark Heller
"Well - I oughta....." -Jackie Gleason

Page 1 of 2 1 2

Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 67
Joined: January 2002
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.028s Queries: 15 (0.003s) Memory: 0.8173 MB (Peak: 0.9908 MB) Zlib enabled. Server Time: 2017-03-29 15:15:18 UTC