#121163 - 06/20/05 01:16 PM What's Right Here?
Admin Online   content

Administrator
Member
Registered: 10/07/00
Posts: 3417
Loc: NY, USA
(submitted via Joe Tedesco)
Quote:
Recieved call rooftop heating&cooling unit not functioning. Upon inspection found somewhat of a problem. Brand new unit, old disconnect manually closing switch would not work. Actually had to close knife blades with insulated handles of linemans pliers.






Top
Tools for Electricians:
#121164 - 06/20/05 04:43 PM Re: What's Right Here?
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
Whats right? It's off!
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#121165 - 06/20/05 05:32 PM Re: What's Right Here?
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
What's right here?.
Well, the Phase Sequence in the top pic looks to be OK.
Not a lot else, though.
I see in the bottom pic that this unit has been "modified" since it left the factory, hence the loose Ground wire.
Unbelievable.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top
#121166 - 06/20/05 05:36 PM Re: What's Right Here?
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
Actually had to close knife blades with insulated handles of linemans pliers.

I certainly hope you don't mean that you energized this.
Top
#121167 - 06/21/05 04:56 PM Re: What's Right Here?
pauluk Offline
Member
Registered: 08/11/01
Posts: 7520
Loc: Norfolk, England
Quote:
Well, the Phase Sequence in the top pic looks to be OK


Mike,
Take off your Commonwealth thinking cap and put on your American one instead......
Top
#121168 - 06/21/05 05:56 PM Re: What's Right Here?
techie Offline
Member
Registered: 05/17/05
Posts: 246
Loc: palo alto, ca usa
What's right.. hmm.. they used wirenuts.. beyond that, it looks pretty hopeless..

lots wrong with it..


poor workmanship
romex
lack of chase nipple/bushing
lack of connector on flex
improper phase color (assuming 3 phase)
improper phase sequence
improper grounding
inoperative equipment
improperly sized wiring?
did I mention the poor workmanship?
Top
#121169 - 06/22/05 11:06 AM Re: What's Right Here?
John Crighton Offline
Member
Registered: 05/16/05
Posts: 177
Loc: Southern California
Too bad the black wire wasn't blue, it would have made pic #1 look so much more patriotic (especially when the fireworks start).

I especially like the way the installer so conscientiously left the romex EGC wrapped in paper (pic #3), so it wouldn't "short" to the box.

On a slightly more serious note... judging from pic #4, is this really 3-phase equipment? The white wire wanders out of the picture, unlike the black and red, which are spliced to the unit primary, so maybe it's really a neutral? If so, why the 3-pole disconnect?
Top
#121170 - 06/26/05 10:24 AM Re: What's Right Here?
mvpmaintman Offline
Member
Registered: 09/15/03
Posts: 123
Loc: Manhattan, Kansas, USA
this looks suspiciosly like one of the local HVAC contractors work -- they always alter the equipment to make it work better :eek
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 90 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals