#121128 - 06/20/05 04:08 PM SE Cable Behind Window Shutter  
Admin  Offline

Administrator
Member
Joined: Oct 2000
Posts: 3,434
NY, USA
(submitted via Joe Tedesco)
Quote
Would you pass this?

I didn't, I red tagged him on poor workmanship.

- JoeRossi
[Linked Image]

[Linked Image]


Tools for Electricians:

#121129 - 06/20/05 07:55 PM Re: SE Cable Behind Window Shutter  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
I cannot tell from the pic if those are real shutters, or simply decorations. Do they operate?


#121130 - 06/20/05 08:12 PM Re: SE Cable Behind Window Shutter  
walrus  Offline
Member
Joined: Jul 2002
Posts: 680
Bangor Me. USA
Looks like a screw in each corner of the shutter to me so I doubt they operate. Not sure why its poor workmanship though? Because it goes behind a fixed shutter??


#121131 - 06/20/05 08:18 PM Re: SE Cable Behind Window Shutter  
Trumpy  Offline


Member
Joined: Jul 2002
Posts: 8,211
SI,New Zealand
Personally,
I'd like to see that service in some sort of conduit.
I'm not sure what SE cable is like around sun-light, but even just for neatness.


Let's face it, these days if you're not young, you're old - Red Green grin

#121132 - 06/20/05 11:45 PM Re: SE Cable Behind Window Shutter  
skingusmc  Offline
Member
Joined: May 2004
Posts: 116
Simi Valley, CA USA
Would this apply:

Art 230.54(C) Service Heads Above Service-Drop Attachment. Service heads and goosenecks in service-entrance cables shall be located above the point of attachment of the service-drop conductors to the building or other structure.

Exception: Where it is impracticable to locate the service head above the point of attachment, the service head location shall be permitted not further than 600 mm (24 in.) from the point of attachment.

From the photo, I can't tell if they "had to" run the point of attaachment right up against the eve of the roof.


Thanks
Steve

#121133 - 06/21/05 02:10 AM Re: SE Cable Behind Window Shutter  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,057
Estero,Fl,usa
The question one of the home inspectors asked was if that drop is rubbing the aluminum facia.


Greg Fretwell

#121134 - 06/21/05 02:28 AM Re: SE Cable Behind Window Shutter  
mxslick  Offline
Member
Joined: Oct 2004
Posts: 803
Atomic City, ID USA
Looks like clearance for the drop from the upstairs window wouldn't be adequate if it was moved to avoid the shutter. (Art. 230-9 1999 NEC)

Also, clearance from the facia may be in violation of 230-24(a) {my extraced quote follows}:

"...The vertical clearance above the roof level shall be maintained for a distance of not less than 3 ft (914mm) in all directions from the edge of the roof. (my bold added)

I realize (before the flaming starts,) [Linked Image] that the reference in 230-24(a) is above but it also says in all directions from the edge of the roof. Another example of doublespeak in the Code, perhaps? In any event, it looks to be too close to the facia.

Reading further, Art 230-26, Point of Attachment seems to apply too.

Good call on the red tag. But I wonder what would be the best way to correct this, short of relocating the meter?

(edited to add smiley)

[This message has been edited by mxslick (edited 06-21-2005).]


Stupid should be painful.

#121135 - 06/21/05 02:43 AM Re: SE Cable Behind Window Shutter  
Trumpy  Offline


Member
Joined: Jul 2002
Posts: 8,211
SI,New Zealand
mxslick,
Quote
I realize (before the flaming starts,)

There's no flaming here, mate. [Linked Image]


Let's face it, these days if you're not young, you're old - Red Green grin

#121136 - 06/21/05 01:47 PM Re: SE Cable Behind Window Shutter  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA


Joe Tedesco, NEC Consultant

#121137 - 06/21/05 09:24 PM Re: SE Cable Behind Window Shutter  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Just a reminder here....everything before the meter is usually regulated by the PoCo's rules, and not the NEC. There are dramatic differences in what those rules are between differing utilities and areas. PoCo rules are also usually much more detailed than the NEC.

As an example, here the use of SE like this is simply not allowed; with a weatherhead like this, you would have to use a mast through the roof eave. Or, you would have three attachment points- one for each conductor.
Also in this area, the service drop is required to be within three feet of the corner of the building.
I am told that other areas have SE as the norm; recently we had another thread of some really ugly such services.

Looking at the pic again- is it possible the meter has already been moved, to move the drop away from that upper window? And- to play devils' advocate- isn't it kind of hard to touch the SE when it is protected by that fake shutter?


Page 1 of 4 1 2 3 4

Member Spotlight
akmaster
akmaster
alaska
Posts: 70
Joined: June 2012
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.020s Queries: 15 (0.002s) Memory: 0.8211 MB (Peak: 0.9982 MB) Zlib enabled. Server Time: 2017-03-25 05:55:13 UTC