#120907 - 05/20/05 05:49 PM Replacing a Range Hood
Admin Offline

Administrator
Member
Registered: 10/07/00
Posts: 3417
Loc: NY, USA
Quote:
Found while replacing a range hood. . . .

(Sometimes handymen aren't really handy. . . .)

The sheet steel in the background is the ductwork for the range hood.

3/4" steel flex coming down from ceiling; which used to feed a cooktop.

The other end of the flex was fed from a 4 x 4 box, with feed-through cover plate, hidden/buried behind a permanently installed wall cabinet 10 feet away.

That is #10 stranded in the flex, spliced with #14 romex.

No j-box or fittings.

The romex grounds are tied to the neutral wire.

One phase fed the range hood, with a 1-amp draw. The other leg fed a duplex outlet that services the counter top.

All this fed by a double-pole 30-Amp Zinsco breaker.

- Tim T.




[This message has been edited by Webmaster (edited 05-20-2005).]
Top
Tools for Electricians:

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 45 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals