The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Topic Options
Rate This Topic
#120812 - 05/06/05 12:17 PM Strip Mall House Panel
Webmaster Offline

Administrator
Member

Registered: 10/07/00
Posts: 3142
Loc: NY, USA
 Quote:
This was a house panel on the back side of a strip mall. I was called out to trouble shoot and repair parking lot lights that were not working. After researching, I found the panel. First the total enclosure had been hit numerous times by trucks. I could barely access it with out pulling it from the wall. The problem, it turns out, was a loose main lug which eventually destroyed the conductor. But, as I looked at all the controls, nothing was right...

The conductors coming from the meter terminated at a 150 amp main breaker. (Barely held on by short screws) >From there the went to a old contactor which was operated by a time clock. The time clock in turn was powered by the load side of the main.(no inline fuse) back to the feeders. From the contactor they terminated to a federal pacific main lug panel. So the whole panel was being shut down during the day. The last 2 pics is what I did to repair it...

- John Cole





Top
Tools for Electricians:
#120813 - 05/07/05 03:12 AM Re: Strip Mall House Panel
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Nice looking rework.

I do have a question, other than the unfused time clock feed whats wrong with shutting the whole panel down by time clock?

Contactor controlled panels are common for lighting circuits.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#120814 - 05/08/05 03:08 AM Re: Strip Mall House Panel
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
I do not want to seem critical here however do I see all the branch neutrals leaving the panel near the top and all the branch hots leaving from the bottom?

This can / will cause the metal enclosure of the panel itself to get warm or hot depending on the load carried by those conductors.

It is also a violation of 300.3(B).
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#120815 - 05/09/05 07:20 AM Re: Strip Mall House Panel
Mike Wescoatt Offline
Member

Registered: 06/17/01
Posts: 164
Loc: Cedar City, Utah
Unless the case is non-ferrous.
_________________________
Mike Wescoatt

Top
#120816 - 05/09/05 10:50 AM Re: Strip Mall House Panel
mxslick Offline
Member

Registered: 10/24/04
Posts: 785
Loc: Atomic City, ID USA
iwire posted:

 Quote:
I do have a question, other than the unfused time clock feed whats wrong with shutting the whole panel down by time clock?


After wondering the same thing and looking at the new installation, my guess would be that the individual contactors on each group of parking circuits would tend to last longer, as the stress of load make/break is distributed instead of concentrated on one contactor.

Also, failure of any one contactor would not leave the entire lot in the dark.

Good call on the hot/neutral separation.
_________________________
Stupid should be painful.

Top
#120817 - 05/10/05 05:35 PM Re: Strip Mall House Panel
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
This isn't a violation of300.3(B)

........contained within the same raceway, auxiliary gutter, cable tray, cablebus assembly, trench, cable, or cord.......

I don't see this as being any of the above.
This is in an enclosure.

It is a violation of 300.20, though. "Induced Currents in Metal Enclosures or Metal Raceways"

Top
#120818 - 05/14/05 03:25 AM Re: Strip Mall House Panel
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
electure

 Quote:
It is a violation of 300.20, though. "Induced Currents in Metal Enclosures or Metal Raceways"


Good point, I gave the wrong reference.

Bob



[This message has been edited by iwire (edited 05-14-2005).]
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals