#120446 - 04/09/05 09:03 PM Lost a Phase, Burnt Meter Pan
Webmaster Offline

Administrator
Member

Registered: 10/07/00
Posts: 3142
Loc: NY, USA
(posted for richard)

the meter with the line side burnt up, probably from water damage







threaded aluminum conduit on roof:






Top
Tools for Electricians:
#120447 - 04/09/05 09:05 PM Re: Lost a Phase, Burnt Meter Pan
Webmaster Offline

Administrator
Member

Registered: 10/07/00
Posts: 3142
Loc: NY, USA
the line to the building. notice (last pics), the point of attachment is on the sign not the building.






Top
#120448 - 04/10/05 08:20 PM Re: Lost a Phase, Burnt Meter Pan
DougW Offline
Member

Registered: 06/08/03
Posts: 1083
Loc: North Chicago, IL
What comes out of the NEMA box on top of the meter base.... power theft point, perhaps?

Top
#120449 - 04/10/05 08:30 PM Re: Lost a Phase, Burnt Meter Pan
NORCAL Offline
Member

Registered: 09/25/02
Posts: 807
Nasty, hacked up electrical, and that roof pond does not look too healthy either.

Top
#120450 - 04/10/05 09:54 PM Re: Lost a Phase, Burnt Meter Pan
mxslick Offline
Member

Registered: 10/24/04
Posts: 785
Loc: Atomic City, ID USA
Very fortunate this didn't evolve phase-to-phase and destroy the riser.

Agree with DougW, what's up with the can above the meter base? Hack substitute for a proper hub maybe?

edit: And is that bypass lever engaged and continuing to feed the building?

[This message has been edited by mxslick (edited 04-11-2005).]
_________________________
Stupid should be painful.

Top
#120451 - 04/10/05 10:34 PM Re: Lost a Phase, Burnt Meter Pan
frenchelectrican Offline

Member

Registered: 02/06/03
Posts: 938
Loc: Wi/ Paris France { France for ...
on the second photo i did notice on main lugs above the socket and i did see the diffrent conductor on left hot line lug look like copper wire is there and the rest is alum wire and this socket this is delta service becaue i can tell by hot conductor with red wild leg on right side of it and also the netrual wire it is copper also so this is very instering set up

Merci, Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


Top
#120452 - 04/11/05 01:36 PM Re: Lost a Phase, Burnt Meter Pan
rad74ss Offline
Member

Registered: 04/19/04
Posts: 154
Loc: Pryor, OK USA
Has anyone checked the gasket on that LB? If that thing starts to crack up due to age/sunlight/heat, the riser turns into a funnel.

I have seen a lot of places with burn outs due to cracked or torn gaskets. Most people don't even think about checking them or changing them out, even though it is relatively cheap versus the cost of replacing whole services.

Robert

Top
#120453 - 04/11/05 03:47 PM Re: Lost a Phase, Burnt Meter Pan
richard Offline
Member

Registered: 08/07/03
Posts: 84
Loc: L.I. New York
i might get a chance to check out that gasket. my boss has to give a price for repair of this mess