#119865 - 02/05/05 12:47 PM SE Cable Installation
Webmaster Offline

Administrator
Member

Registered: 10/07/00
Posts: 3142
Loc: NY, USA
 Quote:
Would this pass 230.70 A (1) "The service disconnecting means shall be installed at a readily accessible location either outside of a building or nearest the point of entrance of service conductors." The cable continues three feet outside the picture and out to the meter.

Electricmanscott

Top
Tools for Electricians:
#119866 - 02/05/05 01:50 PM Re: SE Cable Installation
capt al Offline
Member

Registered: 06/20/04
Posts: 203
Loc: Norton, Ma USA
Electricmanscott, I would say you are right at the limit of Mass Electric Code 230.70 A (1) which allows you to go 10'. Under the NEC I would say this would not pass.
Al

Top
#119867 - 02/05/05 02:09 PM Re: SE Cable Installation
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Al that section requires the disconnect if located outside to be within 10' of building served.

Inside it is still 'nearest the point of entrance'.

As you know I have not done many home services but I thought most of the inspectors are looking for 5' or less?

2002 Mass amendments
 Quote:
230.70(A)(1). Revise to read as
follows:

(1) Readily Accessible Location. The service
disconnecting means shall be installed at a readily accessible location either outside and attached to or within 3 m (10 ft) of the building or structure served, or inside nearest the point of entrance of the service conductors.


In my opinion the wording is tough to decipher.

I have not seen the 2005 amendments, perhaps there is a change.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#119868 - 02/05/05 02:19 PM Re: SE Cable Installation
Electricmanscott Offline
Member

Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
Bob, still reads the same for '05. By the way I did not, and would not install this.


[This message has been edited by Electricmanscott (edited 02-05-2005).]

Top
#119869 - 02/05/05 02:27 PM Re: SE Cable Installation
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Scott

 Quote:
I did not, and would not install this.


He** I knew that.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#119870 - 02/05/05 05:35 PM Re: SE Cable Installation
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
NO...that is beyond the nearest point IMO.

shortcircuit

Top
#119871 - 02/07/05 02:29 PM Re: SE Cable Installation
Steve Miller Offline
Member

Registered: 08/30/01
Posts: 322
Loc: Loudoun Cty, VA
Not a chance on God's green earth (around here)

Top
#119872 - 02/07/05 02:57 PM Re: SE Cable Installation
cpal Offline
Member

Registered: 05/17/04
Posts: 165
Loc: Cohasset MA
Scott

Is the masonary wall clear of obstruction and provides access per 110.26??

No Oil Tanks Etc.Just curious!!

Charlie

Top
#119873 - 02/07/05 03:00 PM Re: SE Cable Installation
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
Wouldn't pass here.
_________________________
Ryan Jackson,
Salt Lake City

Top
#119874 - 02/07/05 03:56 PM Re: SE Cable Installation
velect Offline
Member

Registered: 05/01/04
Posts: 79
Loc: st joseph mi usa
NM stapled on the face of those 2x4's wouldn't pass around here either

Top