#119865 - 02/05/05 12:47 PM SE Cable Installation
Admin Offline

Administrator
Member
Registered: 10/07/00
Posts: 3190
Loc: NY, USA
Quote:
Would this pass 230.70 A (1) "The service disconnecting means shall be installed at a readily accessible location either outside of a building or nearest the point of entrance of service conductors." The cable continues three feet outside the picture and out to the meter.

Electricmanscott
Top
Tools for Electricians:
#119866 - 02/05/05 01:50 PM Re: SE Cable Installation
capt al Offline
Member
Registered: 06/20/04
Posts: 203
Loc: Norton, Ma USA
Electricmanscott, I would say you are right at the limit of Mass Electric Code 230.70 A (1) which allows you to go 10'. Under the NEC I would say this would not pass.
Al
Top
#119867 - 02/05/05 02:09 PM Re: SE Cable Installation
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Al that section requires the disconnect if located outside to be within 10' of building served.

Inside it is still 'nearest the point of entrance'.

As you know I have not done many home services but I thought most of the inspectors are looking for 5' or less?

2002 Mass amendments
Quote:
230.70(A)(1). Revise to read as
follows:

(1) Readily Accessible Location. The service
disconnecting means shall be installed at a readily accessible location either outside and attached to or within 3 m (10 ft) of the building or structure served, or inside nearest the point of entrance of the service conductors.


In my opinion the wording is tough to decipher.

I have not seen the 2005 amendments, perhaps there is a change.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#119868 - 02/05/05 02:19 PM Re: SE Cable Installation
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
Bob, still reads the same for '05. By the way I did not, and would not install this.


[This message has been edited by Electricmanscott (edited 02-05-2005).]
Top
#119869 - 02/05/05 02:27 PM Re: SE Cable Installation
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Scott

Quote:
I did not, and would not install this.


He** I knew that.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#119870 - 02/05/05 05:35 PM Re: SE Cable Installation
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
NO...that is beyond the nearest point IMO.

shortcircuit
Top
#119871 - 02/07/05 02:29 PM Re: SE Cable Installation
Steve Miller Offline
Member
Registered: 08/30/01
Posts: 322
Loc: Loudoun Cty, VA
Not a chance on God's green earth (around here)
Top
#119872 - 02/07/05 02:57 PM Re: SE Cable Installation
cpal Offline
Member
Registered: 05/17/04
Posts: 165
Loc: Cohasset MA
Scott

Is the masonary wall clear of obstruction and provides access per 110.26??

No Oil Tanks Etc.Just curious!!

Charlie
Top
#119873 - 02/07/05 03:00 PM Re: SE Cable Installation
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
Wouldn't pass here.
_________________________
Ryan Jackson,
Salt Lake City
Top
#119874 - 02/07/05 03:56 PM Re: SE Cable Installation
velect Offline
Member
Registered: 05/01/04
Posts: 79
Loc: st joseph mi usa
NM stapled on the face of those 2x4's wouldn't pass around here either
Top
Page 1 of 3 1 2 3 >

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
Today at 02:08 AM
License exam
by TRUE POWER
Yesterday at 09:16 PM
Looking for older post
by sparkyinak
Yesterday at 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals