#119439 - 12/27/04 02:40 PM Hot Circuit
Admin Offline

Administrator
Member
Registered: 10/07/00
Posts: 3417
Loc: NY, USA
Quote:
Came across this in a manufactured home fire recently, and although it did not appear to be the origin of the fire, it looks like it could have been next in line for one.

- codeenforcementguy




Top
Tools for Electricians:
#119440 - 12/27/04 07:03 PM Re: Hot Circuit
mxslick Offline
Member
Registered: 10/24/04
Posts: 803
Loc: Atomic City, ID USA
codeenforcementguy:

Were there other breakers to the left of the burned one? What condition were they in?
And the top breaker on the left side looks like some more melting is happening in the screw area.

Second pic:
At least some of the other breakers appear to have tripped during the fire...

Thermostat pic: Was this the point of origin? I've heard of a few LV t'stats causing fires. If not, what was the cause of the fire?

Waht a sad thing to happen right before Xmas....
_________________________
Stupid should be painful.
Top
#119441 - 12/28/04 06:23 AM Re: Hot Circuit
codeenforcementguy Offline
Member
Registered: 08/27/03
Posts: 29
Loc: Yuma, Arizona USA
Mxslick: No breakers were installed to the left side of the AC breakers. The panel cover was intact and in place, and the knockouts were not disturbed. The thermostat was not the cause, that photo was just to confirm that the settings were in the off position. Cause appeared to be a flammable liquid spill. As my aunt used to say "it appeared to be Arsenic." It was still in the process of investigation at the time I left the scene.
Top
#119442 - 01/02/05 03:18 PM Re: Hot Circuit
Lostazhell Offline
Member
Registered: 02/21/04
Posts: 1428
Loc: Bakersfield, CA (Originally Or...
I've found this a few times when I've pulled breakers out of the ITE style panels... It almost seems like either the contacts in the breaker didnt completely make & they heated up to London Broil temperatures, or corrosion occured between the breaker & the contact stab in the panel & thus lead to a heated connection... I've yet to come across this leading to an actual "structure involved" fire call... But none the less, evidence of that kind of heat having been present does make me think to "double check" all those connections & lugs...

Randy
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 45 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals