#118952 - 11/13/04 07:45 PM Whats Wrong with this Picture?  
Admin  Offline

Administrator
Member
Joined: Oct 2000
Posts: 3,434
NY, USA
Quote
Adding Diesel and Kerosene tanks and related equipment to an already existing gas station. Open up the sub panel to see whats up and imagine my surprise.

Jon aka Walrus
[Linked Image]


Tools for Electricians:

#118953 - 11/14/04 01:11 AM Re: Whats Wrong with this Picture?  
DougW  Offline
Member
Joined: Jun 2003
Posts: 1,143
North Chicago, IL
Lemme guess... the warehouse was out of black wire that day... [Linked Image]


#118954 - 11/14/04 01:58 AM Re: Whats Wrong with this Picture?  
mxslick  Offline
Member
Joined: Oct 2004
Posts: 803
Atomic City, ID USA
Look closely at the "base" of the breakers in question...I see a neutral wire coming into each one. (Top one has curly pigtail, second one a well-weathered [or cooked?] noodle) Since there are no visible test buttons, I would guess that these are breakers designed to interrupt the grounded conductors when tripped.

Isn't that required on fuel dispensing equipment?


Stupid should be painful.

#118955 - 11/14/04 10:00 AM Re: Whats Wrong with this Picture?  
walrus  Offline
Member
Joined: Jul 2002
Posts: 680
Bangor Me. USA
When I opened the panel, I was trying to find out what leg the pump electronics were on so I could phase the new pumps on that same leg. Couldn't understand why I got 120 or 208 no matter where I placed the breaker until I really looked and saw neutral on hot side of the 2 pole switched neutral breaker. Most of have been a friday afternoon job he had phased the stuff right but just placed wires wrong.

Someone with more Electronics knowledge than me explain how this would affect(hot and noodle reversed) power supply in pump??.

Haven't reversed it yet but will on monday after I open gas pumps to make they aren't reversed there also [Linked Image]

Anyone like my lock out tag out yellow tape [Linked Image].


#118956 - 11/14/04 03:56 PM Re: Whats Wrong with this Picture?  
Sir Arcsalot  Offline
Member
Joined: Nov 2003
Posts: 127
Lynden, Washington
These wouldn't be for "white gas" dispensing pumps...?

Seriously, though, this is a NIGHTMARE! Another death waiting to happen :anger:!!!

Edited for typo, etc.

[This message has been edited by Sir Arcsalot (edited 11-14-2004).]


No wire bias here- I'm standing on neutral ground.

#118957 - 11/14/04 09:19 PM Re: Whats Wrong with this Picture?  
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
Could be a QOSWN
http://ecatalog.squared.com/catalog/173/html/sections/06/17306011.html

Switched neutral breaker, not sure if they are required, but should not be reversed. Not sure what damage it could cause, but still not cool.


Mark Heller
"Well - I oughta....." -Jackie Gleason

#118958 - 11/15/04 12:19 AM Re: Whats Wrong with this Picture?  
Sir Arcsalot  Offline
Member
Joined: Nov 2003
Posts: 127
Lynden, Washington
Hmmm... if that IS a switched neutral and required for such a hazardous (classified) location then that red on my face isn't sunburn. Otherwise- grrr!!!


No wire bias here- I'm standing on neutral ground.

#118959 - 11/15/04 03:07 PM Re: Whats Wrong with this Picture?  
safetygem  Offline
Member
Joined: Jan 2002
Posts: 119
Ohio, USA
It could be (although I'm not exactly certain from the photo) that the neutral breakers could be part of the emergency shut-off switch circuit that is required in NEC 514.11. Here is the potentially applicable section in the 2002 handbook.

Quote
514.11 Circuit Disconnects.
(A) General. Each circuit leading to or through dispensing equipment, including equipment for remote pumping systems, shall be provided with a clearly identified and readily accessible switch or other acceptable means, located remote from the dispensing devices, to disconnect simultaneously from the source of supply, all conductors of the circuits, including the grounded conductor, if any.

Handbook Note: Single-pole breakers utilizing handle ties shall not be permitted.
The disconnecting means required by 514.11(A) must be clearly marked and readily accessible. The disconnecting means also must be remote from the dispensing device, so that if an emergency occurs that requires rapid shutdown of the dispensing equipment, the person operating the disconnecting means will not be exposed to the hazard.

It is important to note that all conductors of a circuit, including the grounded conductor, that may be present within a dispensing device must be provided with a switch or special-type circuit breaker that simultaneously disconnects all conductors. Handle ties on single-pole circuit breakers are not permitted. The intent is that no energized conductors are in the dispenser vicinity during maintenance or alteration. Considering possible accidental reversal of the polarities of conductors at panelboards, the grounded conductor must be able to be switched to the open or off position. Grounded conductors may be present in old-style pump motors, or they may pass through a dispenser as part of a circuit for the dispensing island lighting.


514.13 Provisions for Maintenance and Service of Dispensing Equipment.
Each dispensing device shall be provided with a means to remove all external voltage sources, including feedback, during periods of maintenance and service of the dispensing equipment. The location of this means shall be permitted to be other than inside or adjacent to the dispensing device.

Handbook Note: This requirement is intended to enhance the level of safety for personnel servicing dispensing equipment. As more sophisticated control circuitry is integrated into dispensing equipment, simply shutting off the main power source to the dispenser or remote pump does not necessarily ensure that the equipment being worked on has been isolated from all sources of voltage. To ensure that the equipment is completely isolated from all voltage sources, a means must be provided to remove all external voltage sources from each dispensing device, including sources that may backfeed into the dispenser.


You can also check out the requirements in NFPA 30A, which (at least for the time being) is available as a "read-only" free document on the NFPA website. Although, it pretty much says to install according to the NEC.
http://www.nfpa.org/categoryList.asp?categoryID=279


#118960 - 11/15/04 10:49 PM Re: Whats Wrong with this Picture?  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,259
Fullerton, CA USA
Not a shunt trip, is it?


#118961 - 11/16/04 04:35 PM Re: Whats Wrong with this Picture?  
walrus  Offline
Member
Joined: Jul 2002
Posts: 680
Bangor Me. USA
Quote
Couldn't understand why I got 120 or 208 no matter where I placed the breaker until I really looked and saw neutral on hot side of the 2 pole switched neutral breaker
.
After opening pumps to make sure it wasn't reversed there, I fixed the mix up yesterday.Kinda odd as the rest of the job was neat and workman like. I'm sure he/she had a brain cramp [Linked Image]

[This message has been edited by walrus (edited 11-16-2004).]