#118267 - 08/26/04 10:53 AM Marina Telephone Flexible Conduit
Webmaster Offline


Registered: 10/07/00
Posts: 3142
Loc: NY, USA
The attached photos show telephone cable installed in such a way as to make me forget what I was doing and overlook for a time the supports missing on cables. If anyone recognizes the location, please do not state where it is. I asked permission to post these pictures as long as I did not say where they were taken.

1- The flexible conduits (and cables) need supports within 12" of the cabinets and at 3' intervals thereafter across the deck. NEC 350.30, 356.30

2- The flexible cable connection to the receptacle box is damaged and requires support as above. NEC 350.24

3- I should have checked the telephone cabling inside the hose, it must be listed for a wet location. The raceway (garden hose) is not listed for its use. NEC 800.4, 110.3(B), 800.6

4- The receptacles were GFCI protected by a breaker, but the cover was needing to be weatherproof while-in-use. NEC 406.8 (B)(1)


Tools for Electricians:
#118268 - 09/26/04 07:03 PM Re: Marina Telephone Flexible Conduit
Theelectrikid Offline

Registered: 04/30/04
Posts: 854
Loc: Levittown, PA
No, no way... definately no way... Please tell me when the NEC said "Garden hose is a permitted raceway?" (Question not comment.) At least you can do what I know somebody said in another post, "Saving materials by combining water and electrical service." I'd like to see that hose connected to a faucet...