The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
sparkyinak 8
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 220 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#11822 - 07/24/02 08:21 AM Swimming pools(Above ground)
SJT Offline
Member

Registered: 07/24/02
Posts: 242
Loc: PATCHOGUE, N.Y.
On an above ground pool, is the bare #8 that we use supposed to be connected to the equipment ground that is ran out to the pool? The code states that it is not the intent of the code that the bond wire be attached to to any remote panel board, service equipment, or any electrode. Normally what I would do is run the bare #8 to pick up every other upright on a typical 4' high pool, and attach it to the green #12 conductor that is ran to the filter receptacle.
Any problems?
Thanks SJT

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#11823 - 07/24/02 10:40 AM Re: Swimming pools(Above ground)
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
SJT,

Apparently the main concern is that everything in and around the pool be at the same potential. Connecting to the EGC is optional I am told, but you must connect to any associated equipment out there (pump, heater, etc)

Bill

Top
#11824 - 07/24/02 03:33 PM Re: Swimming pools(Above ground)
Electricmanscott Offline
Member

Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
No need to attach to the circuit ground. Connecting to the motor bonding lug actually accomplishes this indirectly. You seem to have it figured out for the pool just run the bond to the motor lug.

Top
#11825 - 07/24/02 10:20 PM Re: Swimming pools(Above ground)
Scott35 Offline

Broom Pusher and
Member

Registered: 10/19/00
Posts: 2724
Loc: Anaheim, CA. USA
FYI - The part in the NEC which mentions no intention for the # 8 to be run to a panel board is simply stating that the bonding conductor does not have to run from a panel, then do all the bonding in an uncut run, just so it's not confused with similar bonding issues.

In other words, the #8 bond does not have to originate from any given panel board, nor is it required to be a dedicated or unspliced run from a panel board to the bonded items.

This [I believe] is to address two separate grounding issues around pools:
1: The EGC for a Pool Light is run uncut from the panel board to the fixture,
2: The bonding of stuff near the pool and the REBAR for the pool is creating an Equipotential Plane, where everything is driven to the same Potential to lower the chance of personnel getting barbequed from either a pump motor winding ground fault, or for the dare devil clowns who float 120 VAC television sets in the pool [reference to Joe's Dishwashing Detergent Bottle / Floating TV set receptacle photo - an ECN classic!].

I don't know if this helps at all.

Scott S.E.T.
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Top
#11826 - 07/25/02 10:10 AM Re: Swimming pools(Above ground)
Frank Cinker Offline
Member

Registered: 07/29/01
Posts: 317
Loc: Pennsylvania
Just a thought. If said above ground pool is storable as defined in Article 680, no bonding is required. Storable Pools: NEC 680.30

Top