#11822 - 07/24/02 08:21 AM Swimming pools(Above ground)
SJT Offline
Member
Registered: 07/24/02
Posts: 242
Loc: PATCHOGUE, N.Y.
On an above ground pool, is the bare #8 that we use supposed to be connected to the equipment ground that is ran out to the pool? The code states that it is not the intent of the code that the bond wire be attached to to any remote panel board, service equipment, or any electrode. Normally what I would do is run the bare #8 to pick up every other upright on a typical 4' high pool, and attach it to the green #12 conductor that is ran to the filter receptacle.
Any problems?
Thanks SJT
Top
Work Gear for Electricians and the Trades
#11823 - 07/24/02 10:40 AM Re: Swimming pools(Above ground)
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 4196
Loc: NY, USA
SJT,

Apparently the main concern is that everything in and around the pool be at the same potential. Connecting to the EGC is optional I am told, but you must connect to any associated equipment out there (pump, heater, etc)

Bill
Top
#11824 - 07/24/02 03:33 PM Re: Swimming pools(Above ground)
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
No need to attach to the circuit ground. Connecting to the motor bonding lug actually accomplishes this indirectly. You seem to have it figured out for the pool just run the bond to the motor lug.
Top
#11825 - 07/24/02 10:20 PM Re: Swimming pools(Above ground)
Scott35 Offline

Broom Pusher and
Member
Registered: 10/19/00
Posts: 2724
Loc: Anaheim, CA. USA
FYI - The part in the NEC which mentions no intention for the # 8 to be run to a panel board is simply stating that the bonding conductor does not have to run from a panel, then do all the bonding in an uncut run, just so it's not confused with similar bonding issues.

In other words, the #8 bond does not have to originate from any given panel board, nor is it required to be a dedicated or unspliced run from a panel board to the bonded items.

This [I believe] is to address two separate grounding issues around pools:
1: The EGC for a Pool Light is run uncut from the panel board to the fixture,
2: The bonding of stuff near the pool and the REBAR for the pool is creating an Equipotential Plane, where everything is driven to the same Potential to lower the chance of personnel getting barbequed from either a pump motor winding ground fault, or for the dare devil clowns who float 120 VAC television sets in the pool [reference to Joe's Dishwashing Detergent Bottle / Floating TV set receptacle photo - an ECN classic!].

I don't know if this helps at all.

Scott S.E.T.
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top
#11826 - 07/25/02 10:10 AM Re: Swimming pools(Above ground)
Frank Cinker Offline
Member
Registered: 07/29/01
Posts: 317
Loc: Pennsylvania
Just a thought. If said above ground pool is storable as defined in Article 680, no bonding is required. Storable Pools: NEC 680.30
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
Today at 02:08 AM
License exam
by TRUE POWER
Yesterday at 09:16 PM
Looking for older post
by sparkyinak
Yesterday at 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
2 registered (dougwells, Admin), 190 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 11/11/05
Posts: 190

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals