The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Topic Options
Rate This Topic
#118117 - 08/12/04 05:35 AM Is this ground bar OK
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
 Quote:
came across this ground bar in a otherwise normal & clean looking panel... I didn't make a huge issue of it to the owner of the store, but I did note it in the contract.....


Randy



Top
Tools for Electricians:
#118118 - 08/12/04 09:09 AM Re: Is this ground bar OK
cpal Offline
Member

Registered: 05/17/04
Posts: 165
Loc: Cohasset MA
Are those sheetmetal screws w/washers??

looks a little shakey 250.8 maybe 110.3 (B)??

Top
#118119 - 08/12/04 09:27 AM Re: Is this ground bar OK
dougwells Offline

Member

Registered: 05/03/03
Posts: 1228
Loc: kamloops BC Canada
those screws are called Wafer teks they are all in in , I would use them mounting boxes to steel studding.

Top
#118120 - 08/12/04 09:31 AM Re: Is this ground bar OK
CTwireman Offline
Member

Registered: 02/07/02
Posts: 839
Loc: Connecticut, USA
Looks like a GE ground bar in a Cutler Hammer panel. Not quite compatible.

Peter
_________________________
Peter

Top
#118121 - 08/12/04 03:01 PM Re: Is this ground bar OK
necbuff Offline
Member

Registered: 07/08/04
Posts: 27
Loc: Lebanon Tn USA
I don't believe this installation is code compliant. Sheet metal screws are not permitted to connect grounding conductors to enclosures. 250.8........... In this case, tek (self tapping) screws.
_________________________
Kenny Wilee

Top
#118122 - 08/12/04 04:13 PM Re: Is this ground bar OK
e57 Offline
Member

Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
Is it me, or does that bar look like it was cut in half for some reason?

If so both are a no-go.
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason

Top
#118123 - 08/12/04 05:47 PM Re: Is this ground bar OK
Sir Arcsalot Offline
Member

Registered: 11/17/03
Posts: 117
Loc: Lynden, Washington
 Quote:
Is it me, or does that bar look like it was cut in half for some reason?


Hmmm... split busses are BAD NEWS any way you look at them!!!!!!!

I just could not resist...!
_________________________
No wire bias here- I'm standing on neutral ground.

Top
#118124 - 08/12/04 10:13 PM Re: Is this ground bar OK
NORCAL Offline
Member

Registered: 09/25/02
Posts: 807
IMO, GE has the worst ground bars around, that split is "normal" for them.

Top
#118125 - 08/13/04 02:43 AM Re: Is this ground bar OK
PCBelarge Offline
Member

Registered: 06/08/03
Posts: 657
Loc: Dobbs Ferry, NY, USA
This poses an interesting situation for inspectors.
Do we violate the installation for not using the proper listed equipment for the enclosure, or do we say at least they separated the equipment grounds from the neutral so I am satisfied?
This is a very typical installation I see almost everyday.
This is clearly a violation of 110.3(B), but...

I will say this; I have seen large faults where the connection of the fittings and the screws were scortched - obviously not a good sign for the fault current path.

Pierre
_________________________
Pierre Belarge

Top
#118126 - 08/13/04 12:46 PM Re: Is this ground bar OK
Lostazhell Offline
Member

Registered: 02/21/04
Posts: 1248
Loc: Bakersfield, CA (Originally Or...
110.3(B) is the first thing that came to mind with me when I saw this also... The thing I mostly was concerned about was that the panel can is being used as the bonding means (No separate EGC coming in with the feeders via EMT). If it comes down to clearing a fault on the 60A 240V A/C circuit which is connected in this panel, will the buttonheads or wafer teks be reliable in doing so?

Could this technically fall under 250.8?

-Randy

-Randy

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals