#117795 - 07/09/04 09:01 AM Is this a Violation?
Admin Offline

Administrator
Member
Registered: 10/07/00
Posts: 3417
Loc: NY, USA
Quote:
Is this a Violation?

- Ron
Top
Tools for Electricians:
#117796 - 07/09/04 12:21 PM Re: Is this a Violation?
pauluk Offline
Member
Registered: 08/11/01
Posts: 7520
Loc: Norfolk, England
I'll hazard a guess that it could be if the connectors were used as a required disconnect for whatever machinery is running on them, as the plugs would not be quickly and easily withdrawable.
Top
#117797 - 07/09/04 12:24 PM Re: Is this a Violation?
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
I was thinking the same thing Paul.

Bill
Top
#117798 - 07/09/04 12:36 PM Re: Is this a Violation?
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
As above, if the caps are the disco, yes, a red sticker.

Also, is this a use of cord that is not compliant with Art 400.7 / 400.8 limitations to usage of cord? As the install is not completly visable, no determination can be made.

If pull out is a problem, the installer should have considered twistlock devices, in lieu of ty-wraps.

John
_________________________
John
Top
#117799 - 07/09/04 02:44 PM Re: Is this a Violation?
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
Also, the sealtite flex doesn't appear to be secured within 12" of the boxes, so yes.
350.30(A)
We're also looking at 225° (at least) of bend just to get out of the center box. Could it possibly exceed 360° between pull points?
350.26
Top
#117800 - 07/09/04 03:01 PM Re: Is this a Violation?
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Generally we use twist locks.

This looks to me like a under a data room floor.

If it is under 645 rules the liquid-tight need not be secured, the same for the box. 645.6(E)

We do a lot of installs where the UPS maker supplies pre-made liquid-tight whips with FS type boxes and receptacles.

For better or worse all you do is drop them in like extension cords.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#117801 - 07/09/04 03:05 PM Re: Is this a Violation?
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
The 3/4" square tube legs that are bonded with the bare copper along with what looks like a piece of fiberoptic cable in the bottom of the picture are what makes me think this is a 645 room.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#117802 - 07/09/04 03:20 PM Re: Is this a Violation?
Ron Offline
Member
Registered: 03/13/02
Posts: 582
Loc: White Plains, NY
Sorry to be away for so much activity.
It is an Article 645 installation. The plugs are for computer servers, not requiring a means of disconnect like a motor.
_________________________
Ron
Top
#117803 - 07/09/04 03:22 PM Re: Is this a Violation?
Ron Offline
Member
Registered: 03/13/02
Posts: 582
Loc: White Plains, NY
The server cords do not have twist lock plugs, hence the straight blade receptacle. No one wants to cut the factory plug off a server.
_________________________
Ron
Top
#117804 - 07/09/04 06:53 PM Re: Is this a Violation?
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
Bob,
Don't you mean 645.5(E)??

Now read 645.5(D)(2)
"installed in accordance with 310.11"
These don't look like a specially listed whip to me.
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
2 registered (gfretwell, sparkyinak), 53 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals