#117477 - 06/18/04 06:21 AM Burnt Receptacle
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
I got a call from my brother in-law yesterday to see why his freezer stopped working.



_________________________
Ryan Jackson,
Salt Lake City
Top
Tools for Electricians:
#117478 - 06/18/04 06:24 AM Re: Burnt Receptacle
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
So what was the problem?


Where you able to get some good conductor into the box?
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#117479 - 06/18/04 06:32 AM Re: Burnt Receptacle
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
Good morning Bob. Yes, they had a switch right above the receptacle, and thanks to poor workmanship, tghe failed cable wasn't stapled to the stud. I was able to hook on some new 12-2 and pull it through. All said I was done in about an hour.

It was sure spooky though, looking at how the wood paneling had already started to discolor and carbonize.
_________________________
Ryan Jackson,
Salt Lake City
Top
#117480 - 06/18/04 07:48 AM Re: Burnt Receptacle
Lostazhell Offline
Member
Registered: 02/21/04
Posts: 1428
Loc: Bakersfield, CA (Originally Or...
Good grief! That looks like it might've been a close one! I hate coming in on things & finding evidence that a burn was actually imminent under existing circumstances.....
Was the Slater push & pray connected or were the side terminals loose? This looks like copper, but I have to ask... Is it?

-Randy
Top
#117481 - 06/18/04 04:33 PM Re: Burnt Receptacle
twh Offline
Member
Registered: 03/11/04
Posts: 901
Loc: Regina, Sask.
See!! That's what happens when you install receptacles upside-down.
Top
#117482 - 06/19/04 07:50 PM Re: Burnt Receptacle
ComputerWizKid Offline
Member
Registered: 09/20/03
Posts: 119
Loc: Connecticut, USA
I hope you replace that cordcap
and did a breaker trip?

[This message has been edited by ComputerWizKid (edited 06-19-2004).]
_________________________
Theres always enough room in the junction box.You just need a bigger hammer
Top
#117483 - 06/19/04 09:37 PM Re: Burnt Receptacle
ThinkGood Offline
Member
Registered: 08/07/02
Posts: 1081
Loc: Milwaukee, WI
The "neutral" is the burnt side here, correct?
Top
#117484 - 06/20/04 06:10 AM Re: Burnt Receptacle
DougW Offline
Member
Registered: 06/08/03
Posts: 1143
Loc: North Chicago, IL
Oh boy Oh boy Oh boy Oh boy Oh boy ..... Talk about lucky!
Top
#117485 - 06/20/04 08:07 AM Re: Burnt Receptacle
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
Yes I did replace the cord cap, and no, the breaker didn't trip...I would assume that is because, as TG pointed out, it was on the nuetral side. The conductors were actually copper. I think what was happening is that, if you notice, the receptacle is very close to the right side of the box. I think it had started arcing from teh nuetral to the box, and it just generated heat.

I'll tell you the scary part though...as I said, this was a relative of mine. There is no denying that this really could have started a fire. I mean, when I cut the paneling a little to install a new cut-in box, it just crumbled...it was that burnt. Anyway, the scary part is that we are all going on vacation next week. I really think that they could have came home from vacation and found that they had no home.
_________________________
Ryan Jackson,
Salt Lake City
Top
#117486 - 06/21/04 04:32 PM Re: Burnt Receptacle
Lostazhell Offline
Member
Registered: 02/21/04
Posts: 1428
Loc: Bakersfield, CA (Originally Or...
Ryan J wrote:

Quote:
I think it had started arcing from teh nuetral to the box, and it just generated heat.


Ryan... Your ground & grounded phase are supposed to be at the same potential! If there was high resistance between the outlet terminal & the actual neutral wire, I can see were you're coming from.. but if you really think this was happening, I'd look a little closer at the service panel neutral/ground bonding & ohm out the neutral back to this point from there to make sure they are, in fact, at the same potential!

-Randy
Top
Page 1 of 3 1 2 3 >

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 45 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals