#116961 - 05/10/04 08:07 AM Too Loose  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,259
Fullerton, CA USA
I'm amazed that this lasted as long as it did!
The 2 lugs on the right were never tightened, and after 25 years I was able to remove the wires from both without any tools...just pull.
The original installer also went to great lengths to install the wrong kind of fuses in the disconnect feeding the panel.

[Linked Image]


[Linked Image]


[Linked Image]

...S


Tools for Electricians:

#116962 - 05/10/04 10:26 PM Re: Too Loose  
Lostazhell  Offline
Member
Joined: Feb 2004
Posts: 1,428
Bakersfield, CA (Originally Or...
Scott,
Is this inside a fusible disconnect for a stand up switchgear? The disco looks like it was meant for something alot beefier than what it was being used for.. the conductors appear to be #2 or #4 THW's, what was the max current rating on the disco? Looking again at those lugs, as chewed up as they are, I get the feeling the installer didn't have the right size allen wrench to torque the lugs right [Linked Image]
Just curious, what size are the fuses & what kinda wierd idea is attached to them to add length? The fuses don't look like they make very good contact on the "unextended" side! [Linked Image] It is pretty amazing this lasted 25 years! Was the load on here just kept really low overtime?

-Randy


#116963 - 05/11/04 12:29 AM Re: Too Loose  
nesparky  Offline
Member
Joined: Jun 2001
Posts: 642
omaha,ne
The lights come on when you turned on a switch. The electrical system must be ok.
Just go to show how forgiving electrical can be. [Linked Image]

[This message has been edited by nesparky (edited 05-11-2004).]


ed

#116964 - 05/12/04 12:07 AM Re: Too Loose  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
Looks like 100-amp class-H-dimension fuses are "teetering" in 200-amp class-H clips.


#116965 - 05/12/04 07:53 AM Re: Too Loose  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,259
Fullerton, CA USA
Well, they actually are 100 amp fuses in a 100 amp disconnect, but...

They're "extremely fast acting" fuses, designed to protect semiconductors (inverters and the like).
They're meant to be bolted into a fuse block,(in which case the writing would show). This goofy guy got fuse reducers, and you can see the results.
Coupled with the fact that the panels are GTE/Sylvania (Zinsco) bolt-in models, the selectivity certainly leaves something to be desired [Linked Image]
In the early life of this panel, it was under a pretty high load, with a lot of incandescent lighting and a 10hp fountain pump.
I noticed the arcing and sizzling sound while standing in front of the panel while it only had a 5 or 10 amp load on it.

Randy, I don't think that an allen wrench was ever applied to these lugs. I think that they were possibly just spun down with a screwdriver...S


#116966 - 05/13/04 01:29 PM Re: Too Loose  
Lostazhell  Offline
Member
Joined: Feb 2004
Posts: 1,428
Bakersfield, CA (Originally Or...
Is it just me, or are the lugs actually loose from the busbars as well! [Linked Image] [Linked Image] They seem to be in different positions in the pics!

-Randy



Member Spotlight
mersadrad
mersadrad
Montreal, Quebec, Canada
Posts: 28
Joined: March 2011
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.014s Queries: 14 (0.003s) Memory: 0.7764 MB (Peak: 0.9238 MB) Zlib enabled. Server Time: 2017-03-26 11:10:53 UTC