How do ya like this?


Top
Tools for Electricians:
#115738 - 12/13/03 07:09 AM Re: Recently Inspected
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Are we looking at Liquidtight Flexible Nonmetallic Conduit?

And I know we are a electrical forum but the post on the left looks substantial so why is it mounted with 5/16" or 3/8" anchors?

[This message has been edited by iwire (edited 12-13-2003).]
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#115739 - 12/13/03 07:46 AM Re: Recently Inspected
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
iwire:
Yes, it's LTNMFC!

The post on the left is a card reader, and the one on the right is a fuel dispenser.
(As to the anchors, maybe they don't want to get sued for a bumper when somebody crashes into one??)

I had to spend a month roving to get gas during the remodel of the fleet station.
This is what I saw when I got back.

I could get pictures of guys smoking cigarettes while pumping gas, filling gas cans in the backs of their trucks, 9 guys in a pickup truck, but I just want to get the heck out of there...S

Top
#115740 - 12/20/03 03:59 AM Re: Recently Inspected
walrus Offline
Member

Registered: 07/25/02
Posts: 671
Loc: Bangor Me. USA
Is the dispenser Gasoline or Diesel fuel??.I've seen worse, at least its not NM feeding the pump

Top
#115741 - 12/20/03 11:23 AM Re: Recently Inspected
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
Is it intended that “99NEC370-23(e) Raceway Supported Enclosure” apply to an Article 501 {apparently flammable-vapor?} installation regarding ‘floating’/otherwise-unsupported junction boxes?




[This message has been edited by Bjarney (edited 12-20-2003).]

Top
#115742 - 12/21/03 01:59 PM Re: Recently Inspected
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
Good Shot, Walrus!
It's a diesel dispenser, about 40 feet away from any gasoline.
I still don't think that this is very safe.
The cheesy plastic conduit is gonna get clobbered. Sooner, not later!

Top
#115743 - 12/21/03 02:58 PM Re: Recently Inspected
CaOperator Offline
Member

Registered: 04/17/03
Posts: 56
Loc: Los Angeles, CA, USA
Ironically, what this type of installation usually suffers from is an employee seeing it as a step stool to clean, and or relamp the dispenser. Or it would not surprise me to find a driver resting his foot on top while entering his passcode into the card reader. This could be made far safer by use of a cover of some sort.

Top
#115744 - 12/27/03 03:31 AM Re: Recently Inspected
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
electure,
Is this sort of Non-Metallic Conduit resistant to attack by Diesel fuel?.
It also looks like them cable ties are the type that aren't UV-rated either.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top