#115144 - 08/19/03 04:29 PM Hot Transformer !!
Admin Offline

Administrator
Member
Registered: 10/07/00
Posts: 3417
Loc: NY, USA
Quote:
This transformer was marked that it needed 6" air space front and rear.

It is heavily loaded 24/7 and the top was to hot to touch.

It was pushed back tight to the wall.

Bob (iwire)
Top
Tools for Electricians:
#115145 - 08/19/03 05:18 PM Re: Hot Transformer !!
Bjarney Offline
Moderator
Registered: 04/10/02
Posts: 2527
Loc: West-Southern Inner-Northeast ...
Understand that {economy} dry-type transformers are often rated at 150°C rise—which means the hottest part of the transformer can run 270°F above room temperature at rated load. Hence, the logic behind the labeled clearance requirement.
Top
#115146 - 08/19/03 05:41 PM Re: Hot Transformer !!
ThinkGood Offline
Member
Registered: 08/07/02
Posts: 1081
Loc: Milwaukee, WI
Did they at least offer you lunch?

Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 67 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals