The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (gfretwell), 129 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 3 1 2 3 >
Topic Options
Rate This Topic
#11490 - 07/14/02 09:17 PM Amps on the water line
Steve T Offline
Member

Registered: 02/14/01
Posts: 312
Loc: Oak Park, IL, USA
I recieved a call from a potential seller of a single family home saying the buyer's inspector measured 4 amps on the water service. Our village does not do single family home sale inspections. The problem could be a loose neutral anywhere on the block. Our plumbing code does not allow plastic water lines. Anyone have a solution for this?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#11491 - 07/14/02 10:24 PM Re: Amps on the water line
sparky66wv Offline
Member

Registered: 11/17/00
Posts: 2339
Loc: West Virginia
Wow...

Allow me to add to your Q...

The way I understand it is that if every house has copper lines between them, and every service is bonded to the lines, then the parellel path cannot be avoided... In fact, good workmanship with strong continuity on the water lines will actually allow more current to flow... They will divide the current between them in inverse proportion to their resistances, so a good connection on the water lines is going hand in hand with the poor connection on the neutral, and a bad neutral isn't always the case either... What's the resistance of 3/4" Copper Pipe per 100 foot or so? How can one relate this resistance to divide the load?

(Psst: Pauluk or Scott35 listening here?)

I figure if ya got current on your grounding electrode conductors, it could be 'cause ya got a really good ground. So, is it a bad thing?
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

Top
#11492 - 07/15/02 03:15 AM Re: Amps on the water line
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
I'll 2nd Virgil's response
(don't U ever sleep?)
and add here....

'Other' Grounding Electrodes can be established, and a plastic coupling can be added to the H2O main to oppose parralleling.

The GEC can be left as is on the house side of the H2O main, as a 'bond'

Top
#11493 - 07/15/02 05:01 AM Re: Amps on the water line
sparky66wv Offline
Member

Registered: 11/17/00
Posts: 2339
Loc: West Virginia
I always thought I slept too much...

Here it's already 8:00 and I'm still drinking my coffee... Joe's probably at the site already and wondering where I am...

I'm like a train, hard to get started and hard to get stopped...

Good thing I'm self employed...

_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

Top
#11494 - 07/15/02 05:45 AM Re: Amps on the water line
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Look here for some information that may be of help:

http://www.awwarf.com/exsums/90702.htm
_________________________
Joe Tedesco, NEC Consultant

Top
#11495 - 07/15/02 06:04 AM Re: Amps on the water line
The Watt Doctor Offline
Member

Registered: 12/23/01
Posts: 443
Loc: Mont Belvieu, TX
Let me tell you a little story that may, or may not shed some light on what could be the problem. A few years ago, an instructor told me of a "strange" situation, and how they solved it. The complaint was that the home owner and his family kept getting shocked by the plumbing system in the house. What really added to the problem was that it would "come and go". One day everything was fine. Then, for some strange reason, someone would get shocked on the kitchen sink, a shower head, etc. This instructor of mine went to investigate, and this is what he found. The plumbing system became hot only when the dishwasher was on. So, they pulled the dishwasher out, and had a look. Whoever installed the dishwasher did not connect the EGC. In fact, he said, that they had cut it off at the outer sheath of the NM cable. On top of that, they ran the NM cable under the frame of the dishwasher (between the floor and the frame). As a result, over time, the dishwasher rubbed a hole in the insulation. When the dishwasher went into the rinse cycle, it would shake alittle, and the frame would come to rest on the hot conductor. Now, here is the other twist. There was no bond between the plumbing system, and the neutral at the service. So, what was the result? No path back to the service for the ground fault. With copper lines connecting all the plumbing equipment, you've got a "hot" plumbing system.
Steve,
Sparky and WV66 know a lot more about residential applications than I do. So, I would consider what they have to say, and while you are out there on site take a look at all the equipment that is connected to the plumbing system, and check for a fault with no return path to the service. Also, check the bond between the plumbing system, and the neutral at the service. If it doesn't exist, bond it, and see if it helps. That bond could cause breaker(s) to trip. If it does, then you will know which equipment is the problem.
I have heard of people doing what Sparky is suggesting, but I've never had the "pleasure" of doing it myself. At least consider what I have to say, and if it works for you, then, more power to you. If it doesn't work........hey, I tried.

Smoke on the water line,
Fire in the sky,
Doc
_________________________
The Watt Doctor
Altura Cogen
Channelview, TX

Top
#11496 - 07/15/02 08:02 AM Re: Amps on the water line
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Sparky, is correct. There will always be current on the metal under ground water piping system in a code compliant installation if the water piping system is common to other buildings connected to the same utility transformer. In some cases, this path via the water piping system may even be a better path than the service neutral. Also remember that the current you are measuring on the water pipe may very well originate in a different building. This current exists even when there are no problems with the service grounded conductor. It will, of course, increase if there is a problem with the service neutral.
_________________________
Don(resqcapt19)

Top
#11497 - 07/15/02 11:55 AM Re: Amps on the water line
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
Yep, if all the water lines are metallic throughout and with multiple grounds at the xfmr and each house, there's bound to be some current flowing on the pipes. How much will depend upon the relative resistances.

We have a similar situation in the U.K. with our PME distrubution system, which is basically the same as the standard U.S. arrangement as far as grouding goes.

In fact the very presence of currents on the pipework with this system resulted in our "code" ruling that a different grounding arrangement must be used in the supplies to gas stations and other similar plants.

Top
#11498 - 07/15/02 04:16 PM Re: Amps on the water line
sparky66wv Offline
Member

Registered: 11/17/00
Posts: 2339
Loc: West Virginia
Joe T.,

Nice Link!

Favorites
Add to Favorites
OK

Thanks!

I was actually right for a change?!?!?

_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

Top
#11499 - 07/15/02 04:27 PM Re: Amps on the water line
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Here's another reason that recognizes the hazard.

250.68(B) Effective Grounding Path. The connection of a grounding electrode conductor or bonding jumper to a grounding electrode shall be made in a manner that will ensure a permanent and effective grounding path.

Where necessary to ensure the grounding path for a metal piping system used as a grounding electrode, effective bonding shall be provided around insulated joints and around any equipment likely to be disconnected for repairs or replacement.

Bonding conductors shall be of sufficient length [not like a banjo string] to permit removal of such equipment while retaining the integrity of the bond.

Reason: To protect the water service technician when they are removing the water meter, otherwise they are sure to get a shock!!
_________________________
Joe Tedesco, NEC Consultant

Top
Page 1 of 3 1 2 3 >



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals