#114204 - 02/06/03 05:47 AM Ground Down Connector
Webmaster Offline

Administrator
Member

Registered: 10/07/00
Posts: 3142
Loc: NY, USA
 Quote:
THIS INSPECTION WAS INTERESTING AS THE CONTRACTOR WORKED VERY HARD TO CREATE A GOOD IMPRESSION AS THE INSTALLATION WAS NEAT AND WITH THE EXCEPTION OF THE GROUND DOWN CONNECTOR (I DON'T BELIEVE IT WAS ELECTRICAL) WAS TO CODE. IF IN FACT THE CONTRACTOR HAD INSTALLED An EQUIPMENT GROUNDING CONDUCTOR INTO THE DISTRIBUTION PANEL SOME CONSIDERATION MAY HAVE BEEN MADE BUT REGARDLESS 110.3B STILL IS QUITE VISIBLE AS THE CONNECTING MEANS WAS GROUND FLUSH WITH THE MAIN DISCONNECT.

Top
Tools for Electricians:
#114205 - 02/06/03 07:36 AM Re: Ground Down Connector
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
??????????????

Top
#114206 - 02/06/03 07:46 AM Re: Ground Down Connector
Scotts Offline
Member

Registered: 01/17/02
Posts: 224
Loc: Ventura, CA, USA
I am with you Redsy, However a comment. I do not like wire ties in a panel. At some point in the future there will have to be some trouble shooting done. Then you have to cut off all the damn wire ties without nicking the insulation to find where the wire goes.

Oh yeah, nice key in the panel.

Scott

Top
#114207 - 02/06/03 08:41 AM Re: Ground Down Connector
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
If I install ty-raps for neatness, I won't cinch them too tight. This provides wire management, while allowing enough movement to trace, remove and re-install conductors.

Top
#114208 - 02/06/03 10:49 AM Re: Ground Down Connector
Pearlfish Offline
Member

Registered: 09/12/02
Posts: 83
Loc: Chicago Ridge, Il, USA
Those square Nylon thingys with the double face tape on them are guaranteed to fall off in a week.

Top
#114209 - 02/06/03 07:04 PM Re: Ground Down Connector
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
I read this post three times, and then read the replies. Does anyone know what the "quote" under the pic means??????????
John
_________________________
John

Top
#114210 - 02/06/03 07:33 PM Re: Ground Down Connector
txsparky Offline
Member

Registered: 05/25/01
Posts: 578
Loc: Magnolia,.Texas U.S.A.
John,
It means that the pipe coming into the back of the box has been ground flush with the back of the panel and therefore has no locknut or grounding bushing so the conduit cannot serve as the ground(there is not a ground wire pulled in with the circuits.)He is saying that the fitting was not an electrical fitting so it did not meet the requirement of 110.3(B) Installation and Use. Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling


[This message has been edited by txsparky (edited 02-06-2003).]
_________________________
Donnie

Top
#114211 - 02/06/03 07:51 PM Re: Ground Down Connector
ElectricAL Offline
Member

Registered: 10/10/01
Posts: 615
Loc: Minneapolis, MN USA
John,

I agree. . .I can't articulate it, but when I look at the "locknut" on the "connector", I can't make sense of what I see.

I mean, this appears to be a 1" "connector" of some sort that I've never seen before. If it's been cut or ground down, it doesn't look like it was reamed.

Then there is the proximity of what appears to be concrete screw (the blue hex head) too close to the "connector" to have adequate purchase on the edge of the hole the 'connector" is in.

I need more information to interpret what I'm seeing.
_________________________
Al Hildenbrand

Top
#114212 - 02/06/03 08:44 PM Re: Ground Down Connector
ThinkGood Offline
Member

Registered: 08/07/02
Posts: 1084
Loc: Milwaukee, WI
In other words, this panel ain't grounded, right?

Is this a sub-panel?

In addition to the comments above relative to nylon ties; nylon ties also make for a very sharp corner if the extra is cut off without rounding the edges:

Top
#114213 - 02/06/03 08:55 PM Re: Ground Down Connector
stamcon Offline
Member

Registered: 03/24/01
Posts: 322
Loc: So San Francisco CA
I was confused by the round "nut/washer". I think the fitting was a set screw connector that had the barrel cut off and is being used as a conduit nipple.