#114090 - 01/03/03 11:12 AM Hot Tub Wiring Diagram
Webmaster Offline

Administrator
Member

Registered: 10/07/00
Posts: 3142
Loc: NY, USA


This is a schematic from a popular hot tub sold here.

The point of interest here is that it is showing #8's from a 50A source.

Comments?
Steve~aka~sparky

Top
Tools for Electricians:
#114091 - 01/03/03 01:31 PM Re: Hot Tub Wiring Diagram
BurnOut Offline
Member

Registered: 12/19/02
Posts: 10
Loc: Long Island, NY
Wow another Long Islander!

Top
#114092 - 01/03/03 03:55 PM Re: Hot Tub Wiring Diagram
ZackDitner Offline
Member

Registered: 10/11/02
Posts: 46
Loc: Kitchener, Ontario, Canada
Don't worry, thats only if it's less than 100 feet..lol

I've seen ranges wired with #8 and 50 amp protection.. Isn't there some kind of exception in that situation?

Top
#114093 - 01/03/03 05:17 PM Re: Hot Tub Wiring Diagram
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Is the hot tub equipment and breaker listed for 75°C? If so #8 is fine.
Don
_________________________
Don(resqcapt19)

Top
#114094 - 01/03/03 07:44 PM Re: Hot Tub Wiring Diagram
circuit man Offline
Member

Registered: 11/05/01
Posts: 287
Loc: saluda,s.c.
hey ya gotta it admit, it says in the diagram "less than 100 FT".

Top
#114095 - 01/04/03 10:00 AM Re: Hot Tub Wiring Diagram
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
Outside installs call for a most installs to go from rx to pvc.

My thought here was that every piece in the chain would need comply to 167 deg F, including bugs, splicing tape,etc...

This becomes a chore to verify.....

My other quiery here is part 4 ( Spas & Hot Tubs) of 680 asking for compliance to parts 1 & 2 of the article, and 680.26's bonding issue w/#8.

As i see it the #8 green applies on the exterior, please correct me if i'm wrong

~yers
Steve aka sparky

Top
#114096 - 01/04/03 01:47 PM Re: Hot Tub Wiring Diagram
lighthouse Offline
Member

Registered: 01/02/03
Posts: 141
Loc: philadelphia pa 19125
steve....i agree with avery one else .that # 8 is good for 40 amps.higher for derating per code. but does the hot tub have a motor or two.

Top
#114097 - 01/04/03 04:42 PM Re: Hot Tub Wiring Diagram
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
yes lighthouse,
the instructions are generic to a number of models, so some may have more than a single motor.

the high draw, at least outside, is the heater...

Top
#114098 - 01/04/03 10:25 PM Re: Hot Tub Wiring Diagram
lighthouse Offline
Member

Registered: 01/02/03
Posts: 141
Loc: philadelphia pa 19125
sparky...ok...this is the way i see it.and if i am wrong please tell me.

the above drawing is correct,since there is a motor involve, the calculations fall under motors an other loads.and here what i came up with.a 1 hp motor 230 volts at 8 amps.x 250%= 20 amps (the 20 amp cb)and (the 30 amp cb )is for the heater.the number # 8 wires feeder= the largest motor 1 hp,fla.8 amps plus 25%, plus all other loads 30 amps heater for a total of 40 amps.and for the 50 breaker,take the largest motor overcurrent device 20 amps plus all other loads 30 amps heater for a total of 50 amps.

Top
#114099 - 01/10/03 03:33 AM Re: Hot Tub Wiring Diagram
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
lighthouse,
i think you nailed it, the whole assembly is predetermined per 430.24, kudos!

Top