#113751 - 09/21/02 09:22 PM Topic: >> Conductor Length at Splices
Admin Offline

Administrator
Member
Registered: 10/07/00
Posts: 3417
Loc: NY, USA
This is often seen where a cable has been cut and must be joined back together or someones' idea of Tapping into a line.
Why is this Bad?

Top
Tools for Electricians:
#113752 - 09/21/02 10:26 PM Re: Topic: >> Conductor Length at Splices
Joule-E Offline
Member
Registered: 08/27/02
Posts: 25
Back wrapped ECG's and short conductors, exposed hots behind wire nuts. Could have been done with 2 junction boxes spread apart with 2 new pieces of NM to give adequate wire for the 3-6 rule.

[This message has been edited by Joule-E (edited 09-22-2002).]
Top
#113753 - 09/22/02 06:12 AM Re: Topic: >> Conductor Length at Splices
mamills Offline
Member
Registered: 11/30/01
Posts: 745
Loc: Wharton, Texas, USA
Violations not withstanding, which Joule-e has already mentioned, this thing must have been VERY difficult to put together!

Mike (mamills)

[This message has been edited by mamills (edited 09-22-2002).]
Top
#113754 - 09/22/02 07:12 PM Re: Topic: >> Conductor Length at Splices
Gwz Offline
Member
Registered: 04/29/02
Posts: 197
assuming 1.5"x4" Octagon box and 14 AWG.
15.5 cubic inches / 2 Cu.In. = 7 14 AWG.

314.16.

4 - 2/C NM = 4x2 = 8 x 2Cu.In. = 16 Cu.In.

4 EGC's = 1 EGC = 2 Cu In.

4 Connectors = 1 connector = 2 Cu.In.

Total Cu.In. = 20 Cu. In..

Box is 4.5 C.In too small.

Plus 250.148(A).

Also looks as though some bare Ungrounded conductor exposed at the wirenut, possible 110.7.

Question 334.24.

Appears box was secured to the wood or maybe just a shadow over the bottom hole of the back of box.

[This message has been edited by Gwz (edited 09-23-2002).]
Top

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 65 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals